Re: 220 HVAC disconnect box clearance
Don
So is going under a kitchen sink to stick your wiggy into the receptacle to see why the disposal is not working.
But it too is a disconnect isn't it? A disconnect with a pull out does not have any live (energized) parts even with the pullout removed that you can come into contact with. and where the pullout sticks in is where you can check for voltage with out any exposure to live parts any more than any receptacle will.
The disconnects in Joe's photo are fused disconnect and would require changing the fuses while energized and exposed parts. these would fall under 110.26.as I listed before.
Here is what I'm getting at.
110.26 (A)(1)
Condition 1 ? Exposed live parts on one side and no live or grounded parts on the other side of the working space, or exposed live parts on both sides effectively guarded by suitable wood or other insulating materials.
Insulated wire or insulated bus-bars operating at not over 300 volts to ground shall not be considered live parts.
As you can see the 3 conditions all require "Exposed Live Parts"
In a pullout disconnect there is no exposed live parts! They are UL listed for use without a dead front. There is no maintenance that can ever be done on these types of disconnects. and if they need to be replaced the manufacture gives explicate instructions to remove all power before working on. so this tells me they are not intended to be serviced while energized.
Here is the info on one of these pullout disconnects:
MilBank U3800 pdf
I also scaned the label into the computer. But I don't have a web page to post it to. but I'll E-Mail it to any one who want's to post it.