roger said:David, how does a shower fixture apply to 230.71(A), 90.4, and a MLO panel?
As far as the mini's, that wouldn't change anything either.
Now, are these instructions part of the Listing and Labeling of the equipment or just the manufacturers CYA?
Roger
I guess I didn't understand what you were asking for.
You're apparently looking for something in the panel labeling that would apply to the type of panel being discussed on this thread and restrict that panels usage. . If that's what you're looking for, how about a label that says, ?Suitable for use as service equipment when not more than six main disconnecting means are provided?. . If this fits as an example of what you were asking for, then following that instruction would be required by 110.3(B). . You would apply the information according to the instructions in the UL Panelboard Listing Guide which says under item #20:
20. A panelboard with the neutral insulated from the enclosure may be marked ?Suitable for use as service equipment when not more than six main disconnecting means are provided? when the following conditions are met:
A. There must be at least one combination of switching units that can be mounted to occupy all available space for switching units; and, whether by using handle ties or similar devices, not more than six main disconnects will result (including factory-installed disconnects).
B. With this combination of switching units, no more than six overcurrent-protective devices will be connected to each ungrounded service conductor.
Note that a panelboard marked ?Suitable for use as service equipment when not more than six main disconnecting means are provided? may permit some combinations of switching units varying in ampere ratings and physical size that would exceed the six disconnect rule on a completely filled panelboard.