Pretty much everything needs an equipment grounding conductor per 250.4(A)(2) & (A)(3). You don't even have to look at the wording issues with 250.32.
A shed is a structureHere is the actual job. Homeowner pulls 240v 100amp 3 wire to a panel mounted on side of shed . Pool installer sets pum, switch leg, etc at panel area. I refuse to connect for pool guy because no egc is present. Homeowner says "his electrician" says I full of pow wow. I know it's wrong but trying to give him screenshot of code section. 250.32 says "serving building or structure" which technically this isn't.
He's questioning whether the shed is relevant since no power enters it; it's all only for the pool.A shed is a structure
Structure…..that which is built
I agreeHe's questioning whether the shed is relevant since no power enters it; it's all only for the pool.
I say the remote panel and its support 'structure' qualifies as a structure even without the shed.
Separate buildingOkay but is the new panel mounted on the same structure as the main panel? Or is this pool panel on a detached structure from the main structure? Sorry I am not clear on it.