250.24
(A)(1) General. "The grounding electrode conductor connection shall be made at any accessible point from the load end of the service drop or service lateral to and including the terminal or bus to which the grounded service conductor is connected at the service disconnecting means."
(A)(2) Outdoor Transformer. "Where the transformer supplying the service is located outside the building, at least one additional grounding connection shall be made from the grounded service conductor to a grounding electrode, either at the transformer or elsewhere outside the building."
My question #1: Let's say I have an outside transformer servicing the building. Regarding 250.24 (A)(2), I am thinking, the service point, the load end of the service lateral, is on the primary side of the outside transformer. Am I not correct?
My question #2: According to 250.24 (A)(1) GEC connection can be made any where between the service point and disconnect, INCLUDING the outdoor transformer's secondary side. Right?
My question #3: So, if I decide to make the GEC connection at the transformer secondary, as permitted by 250.24 (A)(1), rather than at the disconnect, do I need to install another GEC connection either outside or at the transformer per 250.24 (A)(2)?