This is a little write up I give the guys at work to help them understand the terminology of grounding and how to apply the NEC to each purpose
Basically there is 4 grounding terms we have to deal with in the NEC that confuse many electricians,
Grounded Circuit Conductor NEC Article 200 (sometimes can be called a neutral)
Grounding Electrode Conductor (GEC) 250.62-250.86
Equipment Grounding Conductor (EGC) 250.110-250.126
Bonding Conductor 250.90-250.106 and other articles through out the NEC
Knowing the purpose of each is the secret to understanding the how and why of the NEC requirements.
So let’s look at each one, and find the purpose of each.
Some can serve more then one purpose if allowed by the NEC as you will see:
Let’s start with the grounded circuit conductor:
The grounded conductor serves as the return path to the source to complete a circuit, also as a neutral it provides a 0 volt reference point when it is connected as the center point of a center tapped transformer, this is when it is a true neutral.
The NEC requires it to be run with the ungrounded supply conductors of a circuit.
But there are times when it can also serve as an EGC, and/or as a GEC, but this is only allowed ahead of the main service disconnect with the exception of existing ranges and dryers where it can serve as the EGC.
It is intended to have normal mode current on it, that is to say it should have current on it if there is a load on that circuit.
Grounding Electrode Conductor:
is a connection thru one or more electrodes to earth to stabilize the voltage of a system to earth, to protect against voltages of a higher source, and to provide a low impedance path in the event of a lightning strike on the system, is not intended to carry current in a normal mode as it is for a grounded circuit conductor, or is it intended to carry fault current.
Now let me expand on this, there is nothing that says it wont carry normal mode current, or fault current, but that is the effect of a conductor serving a dual role such as ahead of the service disconnect. Or as a bond connection to a water pipe that is also the GEC connection, and a fault happens to the water pipe. As we can see there will be many times a conductor will be installed for a given purpose but will criss cross with serving the purpose of other conductors, but for each purpose it must meet or exceed the NEC requirements for each purpose it will serve.
Equipment Grounding Conductor:
The purpose is to simply carry a return fault current back to the source to facilitate the opening of the short circuit protection device or circuit.
Again it is not intended to have normal mode current on it. Like the grounded circuit conductor it too is also required by the NEC to be run with the circuit conductors it protects, from the MBJ to the load it serves.
Bonding conductor:
Is a conductor that does nothing more then bring two or more conductive surfaces to the same potential, so a difference of potential can not exist between them, it could be a bond between two electrodes as an extension of the GEC, or a bond between two sections of equipments as an extension of the EGC, or it could be neither just an equal potential bond, as used in article 680.
This does not mean it will not carry fault current, nor does it mean it won’t be part of a GEC path way, as in some cases it will serve both.
Once we understand each purpose we can apply the NEC for that purpose, and in the case of a conductor serving more then one purpose, make sure it meets the minimum of each requirement.
If I missed anything let me know