crossman said:The 20 foot length required for a CEE can most certainly be, for example, two 10 foot pieces of rebar connected together with tie wire.
As a matter of fact, twenty 1 foot pieces of rebar in the bottom of the foundation, and tied together with either tie wire or by multiple connections to a GEC would be acceptable as a grounding electrode according to the literal text of the code.
In fact 250.52(A)(3) does NOT!
It does say the electrode consists of at least 20'.