tryinghard said:The reasoning by some that NEC allows an undermined amount of steel tied is bad! This can mean 20 1? steels can be tied in a complete bundle you see the way it?s tied is now debatable
Why is tying steel together to create a 20 foot electrode bad? The whole point of "bonding togeter with the usual steel tie wire" is to create a 20 foot minimum length of rebar.
tryinghard said:I will say most of these are posted to figure out how the steel will be installed yet this is not our trade. Worse yet I don?t want a non-electrician installing electrical.
The steel in the footing is not usually installed by an electrician, but instead by a footing contractor. I don't see attaching to reinforcing steel installed in a footing by others any different than attaching to building steel.
Chris