If you mean two hots and a neutral then yes.Not sure I understand.
An open High leg Delta would still need three primary conductors but only two trannies, no?
If you mean two hots and a neutral then yes.Not sure I understand.
An open High leg Delta would still need three primary conductors but only two trannies, no?
240/480V? Is that a high leg three phase like 3P 120/240V? I've never seen 1P 240/480V.
240/480V? Is that a high leg three phase like 3P 120/240V? I've never seen 1P 240/480V.
If you mean two hots and a neutral then yes.
... in other words, a motor rated for 230/460 will work on a 240V or 480V system, not that there is a 240/480V system. ...
Sorry, I meant feeding an open delta, not coming off a high leg open delta.
Feeding the primary side not coming off the secondary.
Now I'm confused. Two hots and a neutral on the primary side of a open delta, yes.
But I have heard of single phase 240/480. Basically a double voltage 120/240 system. Maybe it was kwired who has mentioned them as used on irrigation pumps/farm use.
What is odd to me is that most of the high leg deltas I can point to exist where 3ph is readily available. I was under the impression high leg deltas are mainly installed where 3ph isnt present, but here it seems to be a matter of adding one transformer to the pole vs 2.
What neutral on the primary?
View attachment 19279
I thought you had to have three wires on the primary side of an open delta, just not necessarily three hots.
There's different reasons for that. I would think the primary ones being they started as an open delta before the area was upgraded to three phase and the fact that wye systems were not always preferred like they are now.
I thought you had to have three wires on the primary side of an open delta, just not necessarily three hots.
:thumbsup:
So I understand that one only needs two hots and a neuter for an open delta, but I dont see the logic in a POCO running two phases and neuter. Why not just run three phases? I guess if they want to make it a MGN is that it?
You are looking at the secondary connections. That document is a little unclear because they show two primary connections, not the third, then they discuss the neutral in context with the secondary. SCL is one of the few places that will derive a 240/120 3 phase 4 wire service from an open delta bank. I had one at my shop in Seattle, it confused people a lot, even me, because it’s somewhat rare. But there STILL must be 3 primary phases. The open delta just saves them the cost of one transformer.Stumbled across Seattle City Light's construction document for open deltas.
http://www.seattle.gov/light/engstd/docs2/0125.02.pdf
It appears they feed them with two hots and neutral, even if they have all 4 wires. They have some good jargon too: "Teaser" and "Lighter" for the transformers
...MOST 230V motors 5 HP and under are designed to allow for 208V input,...
Open delta to delta requires three phases.Okay, I got some people saying that the open delta is fed with two phases and a noodle.
Another just said it is three phases.
Anyone know exactly which is correct?
We all agree that it is only two trannies.
What is odd to me is that most of the high leg deltas I can point to exist where 3ph is readily available. I was under the impression high leg deltas are mainly installed where 3ph isnt present, but here it seems to be a matter of adding one transformer to the pole vs 2.