mivey
A is the high leg and AN is 90 degrees from CN and BN. CN and BN are 180 degrees apart exactly like a center-tapped single phase systen.
AB and CA and BC have a 60 degree separation like any normal three phase system, either wye or delta.
The 120 degree separation is not for line to line phases but is for the line to neutral phases when the neutral is at the middle of the wye configuration. You lose that when the neutral move to the center tap position in a delta.
No. You lose the 120 degree LN relationship in the high-leg delta. The LL phases do maintain the 60 degree separation.
A is the high leg in the posted pic.
90, 180, 90 for LN phases (actually two different phase systems consisting of two 120 volt phases in one system and one 208 volt phase in the other system)
60, 60, 60 for LL phases (three 240 volt phases in one system).
The lines representing the line-line coils meet at a 60 degree angle. That does not mean that the corresponding phasors are 60 degrees apart!
-60 + 180 = 120.
That is true.
GoldDigger corrected my posts. The phasors have their normal 120 degree separation in either the wye or delta system. I got hung up on the angles at the common points and erroneously assigned that to the phasors.
Thanks for correcting that.