kwired
Electron manager
 - NE Nebraska
 - EC
I am going to look deeper on Tuesday about. I opened the back plate and I saw the only the neutral and the two ungrounded (hots) connections. The grounding is missing (no green and no green connected to the neutral) and this installation generates at the basement sub-panel.
In existing 3 "prongs" residential, I jump the grounding to the neutral IF the installation is to the main, but if that goes to the sub, them I add the 4 (grounding) wire and go for the 4 prongs. It is the first time I am looking a high-rise building (18 stories) and I am confused.
Like I said earlier, check with a ohmmeter, some of the newer dryers out there are not quite so obvious that the bonding jumper is in place, I like the old strap better that was only a couple inches long and went directly from the neutral terminal to the frame. Many newer ones have a green wire that is not easy to trace where it ends up but if you check with an ohmmeter it is connected somehow to the neutral terminal, and is usually shipped connected to the green screw where you are to land the EGC if you have a 4 wire cord. If you don't remove this green wire and insulate it you end up making a neutral to ground bond when you plug that dryer in, and defeating the whole purpose of running them separately.