Hey! You should feel right at home with that remark. :thumbsup:The irony is strong.
My thoughts exactly. I think Don is yanking our chains a little bit.Don you are tossing aside basic commonsense in this thread.
Do you really think the CMP that put that rule in place was so removed from the trade they asked for the impossible?
I find the whole notion just silly.
Hey! You should feel right at home with that remark. :thumbsup:
Ooooh suh-nap!The irony is strong.
Your last remark is insinuating that i have not... and you couldn't be more wrong. You have even witnessed a few over the years, but you choose to ignore or forget them so you can harass me of nothing worse than what you yourself commit.Oh I am highly opinionated no doubt of that.
Yet the differance is I can, and have on numerous occasions on this forum clearly admitted I was wrong.
I have never said that common sense has ever been used in writing code rules.My thoughts exactly. I think Don is yanking our chains a little bit.
I have never said that common sense has ever been used in writing code rules.
I have never said that common sense has ever been used in writing code rules.
Yet the differance is I can, and have on numerous occasions on this forum clearly admitted I was wrong.
Maybe I should start. :angel:I have a hard time believing this. :happyno::huh:
Oh I am highly opinionated no doubt of that.
Yet the difference is I can, and have on numerous occasions on this forum clearly admitted I was wrong.
I have a hard time believing this.
Maybe I should start. :angel:
It's a new year after all, ya know. Happy New Year to all (you too, Bob)...
Let me play the devil's advocate here...Two minutes of searching
http://forums.mikeholt.com/showthread.php?t=168941&p=1642684&highlight=I+was+mistaken#post1642684
http://forums.mikeholt.com/showthread.php?t=166681&p=1619986&highlight=wrong#post1619986
http://forums.mikeholt.com/showthread.php?t=162886&p=1580453#post1580453
http://forums.mikeholt.com/showthread.php?t=136745&p=1310299#post1310299
http://forums.mikeholt.com/showthread.php?t=130206&p=1246959&highlight=wrong#post1246959
http://forums.mikeholt.com/showthread.php?t=129569&p=1239614#post1239614
http://forums.mikeholt.com/showthread.php?t=127059&page=2&p=1214180#post1214180
http://forums.mikeholt.com/showthread.php?t=123694&p=1173886#post1173886
http://forums.mikeholt.com/showthread.php?t=123507&p=1171817#post1171817
So here is the thing, when I say I can admit when I am wrong, it is the truth.
I may be grumpy, I may be pain in the rear but I am not a liar.
I am not saying that they actually asked for and intended that...I am just saying that the words they used require that.Never the less I don't believe for a moment that the CMP would ask for what you believe the section requires.
It makes no sense and is not possible to do.
The code was changed for the 1990 code and the new language for 346.11 in the 1990 code is identical to the language in 344.26 in the 2014 code.346.11 Bends - Number in One Run. A run of conduit between outlet and outlet, fitting and fitting, or outlet and fitting shall not contain more than the equivalent of four quarter bends (360 degrees, total), including those bends located immediately at the the outlet of fitting.
As far as the original question, I really don't see any real world issue with inductive heating where all of the conductors are within the same ferrous metal conductors, but I see the first and second sentences of 300.20(A) as standing alone, and the second gives a prescriptive requirement, that the conductors be grouped without exception.
I am not saying that they actually asked for and intended that...I am just saying that the words they used require that. . .
So in this case, I am just saying that the actual code language...the enforceable rule...does not reflect the intent of the rule.
Let's agree that the code as written results in unintended interpretation and that it could be worded better.
I think it moved on to the requirement that the conductors be grouped within the enclosure and what "grouped" means.
I agree. Twisted is just one form of grouping.
Here's what I believe to be the intent, and a simple fix in the process.I agree also. The NEC uses the word grouped but as evident in this thread that one word can be interpreted to mean far reaching ridiculous things.
300.20 Induced Currents in Ferrous Metal Enclosures
or Ferrous Metal Raceways.
(A) Conductors Grouped Together. Where conductors
carrying alternating current are installed in ferrous metal
enclosures or ferrous metal raceways, they shall be arranged
so as to avoid heating the surrounding ferrous metal
by induction. To accomplish this, all phase conductors and,
where used, the grounded conductor and all equipment
grounding conductors shall be grouped together in
accordance with 300.3(B).
Here's what I believe to be the intent, and a simple fix in the process.
300.20 Induced Currents in Ferrous Metal Enclosures
or Ferrous Metal Raceways.
(A) Conductors Grouped Together. Where conductors
carrying alternating current are installed in ferrous metal
enclosures or ferrous metal raceways, they shall be arranged
so as to avoid heating the surrounding ferrous metal
by induction. To accomplish this, all phase conductors and,
where used, the grounded conductor and all equipment
grounding conductors shall comply with 300.3(B).