:?:blink:Al,
We are not going to agree on this issue...there is just no way that wires run down one wireway are grouped with the wires in the opposite wireway (my opinion and it is not going to change).
Don, I agreed with you on this "issue" in Post # 109. AND, if there actually was a panel with ONLY one conductor down one side, and ONLY one conductor down the other side, AND the ferrous metal, at a point or area, WAS HEATING, then you have a failure of arrangement per 300.20(A).
HOWEVER, the NFPA Glossary of Terms makes the arrangement, so described (one wire this side, one wire that side), as "grouped" if they share the same ferrous metal container, be the container a raceway or a panel box.
It might be nice if the Rule was prescriptive, but at present, the presence of HEAT is the performance basis for failure to comply, . . . as written, in my opinion.
The complex summing of magnetic fields in open air and in ferrous metal, where the magnetic fields arise from alternating currents in many conductors and where the ferrous metal is of unknown shape, size and orientation relative to the currents, will elude verbal prescription because of the difficulty of measuring and interpreting the magnetic field information, and reducing that to a sentence or two.