My NEC handbook seems to ne in error
The books calculation for 6 EGC, 2 being pigtailed are calculated at 1 volume allowance based on largest 12 AWG conductor at 2.25?
Unless 2 x equipment ground conductor jumpers follow different rules
1) 4X EGC = 2.25 (1 single volume allowance)
2) 2 x EGC (pig tail jumpets) 1/4 x 2 x 2.25
Add 1) + 2) 3.37 total EGC Fill but not 2.25 stated in book?
The books calculation for 6 EGC, 2 being pigtailed are calculated at 1 volume allowance based on largest 12 AWG conductor at 2.25?
Unless 2 x equipment ground conductor jumpers follow different rules
1) 4X EGC = 2.25 (1 single volume allowance)
2) 2 x EGC (pig tail jumpets) 1/4 x 2 x 2.25
Add 1) + 2) 3.37 total EGC Fill but not 2.25 stated in book?