Fitzdrew516
- Cincinnati, OH
You need to calculate load before you know what minimum size service disconnecting means is necessary.
When sizing conductors and overcurrent devices for an individual load it is simpler - that load is either continuous and 125% rule applies or it is not continuous - if using a standard overcurrent device. If using a 100% rated device there is no 125% to deal with.
Multiple loads of same type is sometimes a little more complex but somewhat similar - maybe a feeder that only supplies motors fits this category.
If you are using art 220 for calculating multiple loads then you have already factored in where needed 125% for continuous loads, and in some cases reduced the load because of allowable demand factors. If your result is 375 amps then you need a 375 amp minimum conductor and 375 amp minimum overcurrent device. You likely go next standard size higher which is 400 amps with overcurrent and the conductor will depend on ampacity adjustments that may be required on top of base ampacity.
Yes. I'm saying if your combined calculated load could be over 400A because a "100% rated breaker" is really just a breaker rated for 100% of continuous loads and therefore you could argue the opposite is true and that it is rated for 125% of non-continuous load.
Let's use the example Jumper posted earlier -
200A non continuous load plus 160A continuous load would be a calculated load of 400 amps. So this would be sufficient for a regular old "80% rated breaker" (btw I hate calling them that bc it is what adds to people's confusion).
However, if you were to use a 100% rated breaker then since it is rated for 100% continuous use isn't that the same as it being rated for 125% of non-continuous use? Then I could technically add 100A more (non-continuous) load onto this service. Then we would size the wire to the calculated load which would be 300A non-continuous load + 160A continuous load = 500A.