peter d
- New England
Even with loops (of a reasonable length) being made, is anyone really observing problems with this? :huh:
1965 NEC
336-5. Supports. Nonmetallic sheathed cable shall be secured by approved staples, straps, or similar fittings, so designed and installed as not to injure the cable. Cable shall be secured in place at intervals not exceeding 4 1/2 feet and within 12 inches from every cabinet, box or fitting, except that in concealed work in finished buildings or finished panels for prefabricated buildings where such supporting is impracticable, the cable may be fished between points of access.
I sat for my first journeyman license at a test under the 1965 NEC.
Back then, NM was in 336, and the support rule was in 336-5:
The key phrase is essentially identical to today's 2014 NEC 334.30
No -- I don't think it is an issue. The issue is the interpretation. I did get turned down because I had a staple 13" from the recessed can but that was 30 years ago. It was 24" trusses with the can's jb out toward the middle. I laughed and told him I wasn't going to change a staple for 1". It passed....LOLEven with loops (of a reasonable length) being made, is anyone really observing problems with this? :huh:
We do not dismiss quickly generations of our piers understanding of a particular section no more than we dismiss hastily an electrician’s point of view.
I apprenticed at the side of my old Master, Paul Denny, and he taught me that it was about the length of the NM. The teaching was entirely hands on, with verbal back and forth, as I was his only employee. I read the NEC on my own.Curious, what were you taught or what did you think the rule required back in 1968 under the 1965 code cycle. Do you know what they are teaching journeyman today on the subject?
But you will dismiss the people who write the code when it is not what you want to believe.
Which side of the cable??This can be easily rectified if the cmp had written: "measured along the cable."
Perhaps we are not talking about the same situation. IMO, 334.30(C) requires at least 12" for boxes that are integral with a device. This is could be in areas such as trailers where the receptacle and box is an integral unit. There must be the 12" loop in order for the box to be worked on properly. Also, there are recessed cans where the box is integral with the fixture enclose as in some wac fixtures. Here you need at least a 12" loop-- we just did some of these and there is no way to service them without the loop.
The way I read the proposal was that the submitter was trying to get the proposal for fixtures as well. There was no need so the cmp said that it was already in place. They are not clear about the specifics. Halo recessed cans do not need a service loop as the box is accessible thru the opening. IMO, there is no allowance for more than 12" of cable between the staple and the box. In that same section 334.30, by many people's interpretation, we could leave large loops of wire between the 4'6" distance between staples. Seriously, if you were an inspector would you allow 3' loops between staples?
I can say this with certainty, NC will not allow it- although some inspectors may- I had our state engineering dept look at this thread and he agrees with me...FWIW
As before, that 334.30(C) requires a 12" service loop but B prohibits it makes zero sense. The only time where they possibly arent permitted is in exposed construction where the NM must closely follow the surface of the building.
I am using the 4' because nm must be stapled every 4'-- so the rule for a staple 12" from a box is assinine if 4' is allow to be looped.
Every 4 1/2 feet.
I agree, I see it as asinine too.
BUT, the CMP clearly stated it's allowed.
Please go back and look at the ROP I posted, the panel statement is aimed at all of 334.30, not just one of the subsections.
Bob, both I and our state engineer read it independently and disagree with you as to what the cmp is saying. I believe their response is to (C) where it is allowed to have more than 12" under the scenario where the box is part of the luminaire and you need the service loop.
Anyway, we will, of course bring it up at our annual meeting for whatever it is worth