Electricalguy
- Pennsylvania
- Electrician
I am working on trying to get an new induction heater to turn on. I have a 480 volt 60 amp 3 phase feed coming from my main breaker box. My 60 amp 3 phase breaker is then going a disconnect since my breaker box is not line of site. The 480 disconnect is powering a step down delta transformer 480 volt to 380 volt and has no neutral or ground terminal on transformer just chassis ground. We ran power wires from the 380 lugs and a wire from chassis ground to the induction heater inlet power terminal on the unit. There is a ground stud on the chassis of the induction heater but we did not hook up a ground to this terminal. it seems there is no connection from the ground coming in to the unit to this ground stud. When I meter from phase to phase I get 380 from a to b, a to c and b to c. When I go from metal reference on the chassis I got 150 on phase a 201 on b and 280 on c terminal. The machine is looking for a 220 volt lead from terminal a on the supply. With only 150 volts on a terminal it won't power up. If I were to run a ground from the chassis/breaker box to the ground terminal of the induction heater that would also be common to the transformer would this level out my power on all three terminals to 220 and turn the induction heater on? If the chassis had to be grounded to eliminate any potential charge why would they not just tie in the ground from the supply source or should this be separate ground like to rods outside or such? The building is cinder block so there is no structural steel to tie to. Any thoughts?