Smash
- Philadelphia suburbs, PA USA
Having trouble keeping a 3 phase 208V 5hp motor running. This is for and exhaust fan use for auto exhaust. Voltage reads low between legs 1 & 3 at around 198V all other readings are consistent at 208. This is a car dealership with a large service area. Also has had its share of bad contractors over the years. Things are not labeled correctly and some overall bad work. I believe the voltage problem I'm having is from unbalanced load across the 3 phases. Single phase loads & even 120V loads share this panel. Contractors would just twin up anything to get there job done. I know this unbalance is well past the 2% acceptable limit. My question is how do I balance the load on this panel if the loads are distributed around the large 13 bay service area. There will never be a consistent load when loads are being used at different times. My motor is not real happy with this voltage and trips the 3 phase breaker within minutes. The place is at compacity power wise and is always an adventure looking for a place to pull power for anything. So finding any available clean power is futile. I even pulled the motor had it serviced and there is no problem. Has to be unbalanced load on this 3 phase 4 wire service. What options do I have ? Spending 2K on a special wound 200V motor probably isn't an option. Ty