Correct that it seldom is all going at one time. But there is occasions when it is.not very unusual to have 3 heat pump w/ 10-15kw heat strips each, 2 water heaters, clothes dryer, electric range, etc.
So not very likely for all this to be going at the same time?
Well it is upon family's return from vacation
Ignorant Brit.............
What kind of residence needs a 400A service?
Typically here we have 40A or 60A.
And this is why I despise reading the NEC. It says little and references itself ad nauseum.
Service conductors entering a building shall be installed in accordance with 230.6 or protected by a raceway method identified in 230.43.
230.43 says Service Entrance Cable is good to go....kind of. It says "Service entrance cable is ok if you use the applicable parts of this code".
230.6 seems to be irrelevant (determining if conductors entering a building are outside of a building?)
By that, exposed service entrance cable should be a-ok.
Of course, there's the "if subject to physical damage" caveat, which appears to be left to the whims of the individual inspector.
Hi, I am hoping some one has some pics of a 400 amp service they have done( and are willing to post). This will be my first one. I was wanting to come out of the meter can with two sets of 4/0 alum SE cable with side by side 200 panels directly behind meter can. All the pics i can find all have pvc or have a gutter put in. I was hoping to see how it looks before going ahead. Thanks
Well, yes.I have single breakers that big![]()
Then we need to look at 230.43 which spells out service entrance cable as a method. No whims involved.I would not consider SER cable a raceway & inspectors should not inspect using whims as code but should read the code for what it says
Well, yes.
I've engineered systems with breakers rated at 2000A.
But not for residential applications.
still didn't read - yes - SER Cable is in 230.43 but you shall use a raceway to protect it so your statement of "By that, exposed service entrance cable should be a-ok" is not correct & if you keep the ser outside of the building it in underground raceway it is not compliant.
http://www.milbankworks.com/catalogs/u5890-5895.pdf
Check with utility and ahj, but I have used one of these (very similar anyway) for a 400A residence, to feed two 200A load centers. (if I recall correctly the one I used had one breaker on each side)
It's a Milbank 320 meter socket/combo with two 200A breakers
But very few of those US households are on a 120 volt two wire supply, they are on 120/240 or 120/208 multiwire supplies and the 120 volt load is somewhat balanced across the higher voltage. Net VA for houses with similar appliances is still similar.Could a difference be that your loads are all 230V while most US household loads are 120V?
The issue is that 230.43 has nothing to do with raceways. The word "raceway" doesn't even appear. So after multiple references to other paragraphs, we end up on one that's irrelevant for the purpose for which it was referenced.
Unless, of course, we look at 230.43 and realise that service entrance cables are mentioned in the same list as pretty much every sort of "conduit" available. Regardless of the topic, that would suggest that, for example, ENT and SE cables are equivalent in the eyes of the code in some circumstances.
I now have no clue on the point you are trying to make & it has no bearing on my comments, you seem to not comprehend the meaning I am trying to convey -- so "you win" ---
If the inside 200 amp breakers are your service disconnect 230.32
It seems as though the code would suggest that you are using whims as code, since the actual code you referenced does not say or suggest “SER is not considered a raceway”. I would think a reasonable person of average intelligence would discern from that limited extract of NEC that SER is, indeed, a raceway method.I would not consider SER cable a raceway & inspectors should not inspect using whims as code but should read the code for what it says
Some places maybe have local amendments restricting use of SE cable. Otherwise my simple reply is -why is it called Service Entrance Cable if it can't be used for service entrance purposes?:huh:Interesting, since I'm not trying to "win". I'm merely trying to understand my original question pertaining to the appropriate means of transmitting electrons from a meter box on the outside of a wall, to an electrical panel on the opposite side, and back. I'll recap for you, so you can perhaps see where my question is at and where the code is/is not providing useful information.
You said
Indeed they are 200A breakers.
Let’s see if 230.32 answer the question asked:
The question was: Does 4/0 (SE) exposed really cut it? Does it need to be in a conduit?
Alternately stated: If I run 4/0 Aluminum SE, does it need to be in a conduit?
Actually, 230.32 provides no new information that’s not found elsewhere. It actually says, in so many words, “go away, this isn’t where to find the information you came here for”:
230.32: “Service conductors entering a building or other structure shall be installed in accordance with 230.6 or protected by a raceway wiring method identified in 230.43”
So off we go with 2 places to check.
Let’s look first at 230.6:
230.6 Conductors Considered Outside the Building
Conductors shall be considered outside of a building or other structure under any of the following conditions:
(1) Where installed under not less than 50 mm (2 in.) of concrete beneath a building or other structure.
(2) Where installed within a building or other structure in a raceway that is encased in concrete or brick not less than 50 mm (2 in.) thick
(3) Where installed in any vault that meets the construction requirements of Article 450, Part III
(4) Where installed in conduit and under not less than 450 mm (18 in.) of earth beneath a building or other structure
(5) Where installed in overhead service masts on the outside surface of the building travelling through the eave of that building to meet the requirements of 230.24.
Hmmm…”shall be installed in accordance with 230.6”
Actually, 230.6 merely categorizes methods of installation and answers the question “If I do X, are my conductors considered outside of the building?”
Am I interested in knowing whether or not my conductors are considered outside of the building? Not so much. Therefore, it’s straightforward to conclude that 230.6 does not provide immediately relevant information to answer the question “If I run 4/0 Aluminum SE, does it need to be in a conduit?”
The best I can tell so far, is that my exposed 4/0 SE is probably considered “outside the building” per 230.6. Good to know? Must be.
So knowing that my exposed 4/0 is “outside the building” I’m back looking at 230.32. The first part was useless as a direct answer to my question, so let’s head off on a quest of looking at 230.43. Surely it has the nugget that we need….. “protected by a raceway wiring method identified in 230.43”. Raceway wiring methods. That’s the ticket!
230.43 Wiring Methods for 600 volts, Nominal, or Less
Service entrance conductors shall be installed in accordance with the applicable requirements of this Code covering the type of wiring method used and shall be limited to the following methods:
(1) Open wiring on insulators
(2) Type IGS cable
(3) Rigid Metal Conduit
(4) Intermediate Metal Conduit
(5) Electrical Metallic Tubing
(6) Electrical Nonmetallic Tubing (ENT)
(7) Service-entrance cables
(8) Wireways
(9) Busways
(10) Auxillary gutters
(11) Rigid Polyvinyl Chloride conduit (PVC)
(12) Cablebus
(13) Type MC Cable
(14) Mineral-Insulated, metal-sheathed cable
(15) Flexible metal conduit not over 1.8 m (6 ft) long or liquidtight flexible metal conduit not over 1.8 m (6 ft) long between raceways, or between raceway and service equipment bonduing jumper routed with the flexible metal conduit according to the provisions of 250.102(A), (B), (C), and (E)
(16) Liquidtight flexible nonmetallic conduit
(17) High density polyethylene conduit (HDPE)
(18) Nonmetallic underground conduit with conductors (NUCC)
(19) Reinforced thermosetting resin conduit (RTRC)
Quite a mouthful there.
So having determined from 230.6 that I have conductors that are considered outside of a building, 230.43 tells me that that among the varied list of wiring methods (which are actually just means of protecting wires, and not methods of wiring, but that’s semantics) that SERVICE ENTRANCE CABLES are good to go. Interestingly enough, it makes no reference to “outside the building”.
Does it tell me that they need to be in a conduit? Nope. 230.43 doesn’t even mention the word “raceway”, which is odd since 230.32 seemed to think it was leading me to a list of “raceway wiring methods”. Perhaps I’m to conclude based on the text of 230.32 that the list in 230.43 are ALL considered “raceway” methods.
So from all of that jumping around, I’ve concluded:
1) My conductors are outside of the building
2) Service Entrance Cable is listed among approved wiring methods for service-entrance conductors for under 600 volts.
You proclaimed that
In other words, the code suggests that you were mistaken with your consideration of SER.
Perhaps it’s not permitted by some other section?
My question is protected from what?simply if the 200 amp breakers are inside the building then the wiring method to reach them is also inside -- never said SER could not be used but if it was it would be protected once it entered the building. The service drop to the meter was not part of my comments I was describing the wiring method on the line side of the meter but the continuation to interior service disconnects was my intended discussion to your "By that, exposed service entrance cable should be a-ok" -- the only reason 230.6 was involved was due to interior service disconnects which became the topic of discussion IMO -- the question as I saw it was about wiring methods to inside service disconnects - Thank you for clarifying your view
The meter is rated 320 amp. There are two 200 amp breakers. Is this a 320 amp service or a 400 amp service? When doing the load calc does it have to be 320 amps or less to use this equipment? :?
And if the load is more then 320 amps (regardless of occupancy type or voltage/number of phases) most POCO's seem to prefer CT metering even if there is self contained metering available for the application. Less components for them to have to keep in stock is likely one of the main reasons.This was a very long time ago.... I believe it was the case that the utility company told us "this is how we do 400A residential metering" but I also doubt that the load calc was over 320A. Part of the reason I threw in the note to check with your ahj, they might want to see a load calc, and if they insist on a higher rated meter socket than 320A you may have to go back to the utility company and see what they have to offer as a solution. Basically get your ducks in a row before buying/installing.