Hi, I am hoping some one has some pics of a 400 amp service they have done( and are willing to post). This will be my first one. I was wanting to come out of the meter can with two sets of 4/0 alum SE cable with side by side 200 panels directly behind meter can. All the pics i can find all have pvc or have a gutter put in. I was hoping to see how it looks before going ahead. Thanks
I can see now that this can also be looked at as a free standing service which you are discussing & not mounted on a exterior structure wall which I was discussing
So lets discuss your view with what little we know about this free standing service --
338.12 Uses Not Permitted. (A) Service-Entrance Cable. Service-entrance cable (SE) shall not be used under the following conditions or in the following locations:
(1) Where subject to physical damage unless protected in accordance with 230.50(B) --
This is now a judgement call as subject to physical damage is not a specifically defined location in the Code, If not needed, then the raceway's listed are not required which now comes to full circle of your comment "which appears to be left to the whims of the individual inspector."
230.50 Protection Against Physical Damage
(B)Service-Entrance Cables. Service-entrance cables, where subject to physical damage, shall be protected by any of the following:
(1) Rigid metal conduit (RMC)
(2) Intermediate metal conduit (IMC)
(3) Schedule 80 PVC conduit
(4) Electrical metallic tubing (EMT)
(5) Reinforced thermosetting resin conduit (RTRC)
(6) Other approved means
(2) Underground with or without a raceway
(3) For exterior branch circuits and feeder wiring unless the installation complies with the provisions of Part I of Article 225 and is supported in accordance with 334.30 or is used as messenger-supported wiring as permitted in Part II of Article 396
Part I of Article 225 -- does not apply as this is not on a exterior structure wall
225.10 Wiring on Buildings (or Other Structures). The installation of outside wiring on surfaces of buildings (or other structures) shall be permitted for circuits not exceeding 1000 volts, nominal, as the following:
(1) Auxiliary gutters
(2) Busways
(3) Cable trays
(4) Cablebus
(5) Electrical metallic tubing (EMT)
(6) Flexible metal conduit (FMC)
(7) Intermediate metal conduit (IMC)
(8) Liquidtight flexible metal conduit (LFMC)
(9) Liquidtight flexible nonmetallic conduit (LFNC)
(10) Messenger-supported wiring
(11)
Multiconductor cable
(12) Open wiring on insulators
(13) Reinforced thermosetting resin conduit (RTRC)
(14) Rigid metal conduit (RMC)
(15) Rigid polyvinyl chloride conduit (PVC)
(16) Type MC cable
(17) Type MI cable
(18) Type UF cable
(19) Wireways
simply
if the 200 amp breakers are
inside the building then the wiring method to reach them is also inside -- never said SER could not be used but if it was it would be protected once it entered the building. The service drop to the meter was not part of my comments I was describing the wiring method on the line side of the meter but the continuation to interior service disconnects was my intended discussion to your
"By that, exposed service entrance cable should be a-ok" -- the only reason 230.6 was involved was due to interior service disconnects which became the topic of discussion IMO -- the question as I saw it was about wiring methods to inside service disconnects - Thank you for clarifying your view