electrofelon
Senior Member
- Location
- Cherry Valley NY, Seattle, WA
Lets assume the switchboard will be directly connected to rebar ufer ground.
Bond that ground back to the metal case of the trafo. Run one insulated Cu grd wire in with the neutrals.
I am not sure why you want to run a ground back to the transformer (true we dont know for sure it is a service and not a SDS, but your comment about connecting the UFER to the switchboard strongly implies that you are assuming the service disconnect(s) are in the switchboard). The utility transformer would not be under the NEC, and besides the transformer case would be bonded to the XO (even if the NEC applied, see 250.92(B)(1)).