4000 amp 480v 3ph switch gear

Status
Not open for further replies.

kwired

Electron manager
Location
NE Nebraska
That is a clean installation but could have been done by sets too
the conductors were derated since >3, correct?
does the cond area < 20% cnd area? How long was the run? In feet
short no big difference, long Cu and cnd add up fast
you have 8 cnd = 8 sets, could have rotated cnd 90 deg and been pretty clean
could have possibly used 6 smaller sets (conductor and cnd at 40% fill) without derating?
easier manipulating into position then

there is no right or wrong, these are preferences and judgement
as long as code compliant doesn't matter
But look at how much easier it was to get all conductors of same phase the same length by doing it that way. Now you have to justify cost of that vs, being able to go with smaller conductors if you put all three phases and neutral in each raceway, if it is about a wash then what was pictured will likely win out.
 

Phil Corso

Senior Member
And why do you think that? If the non metallic-raceways are run in close proximity to one another it doesn't matter anyways.Roger

Roger...

Because the phases are separated there is a greater impact of inductivity caused by phase-separation, thereby increasing the "effective resistance"! The result is higher losses than when the 3-phase conductors are bundled in groups of three (tre-foil).

The added "resistance" increase varies as conductor-size increases! For example, up to say #4 AWG (cu), the increase is nil! But for 250 kcmil, the increase is appreciable. If configuration is tre-foil, and operated near rated-current, resistance is r-Ohm/k-ft, but if arranged with separation of say 5-diameters shown in photo (my guesstimate) effective-resistance will increase by 1.05-1.15 x r-Oms/k-ft (an increase of 5-15%!

Phil
 

iwire

Moderator
Staff member
Location
Massachusetts
That is a clean installation but could have been done by sets too
the conductors were derated since >3, correct?

That particular instillation was not mine.

I have done two 3,000 amp services using 8 sets of 600 CU in isolated phases. In my case I had far less room between the floor and the lugs so crisscrossing 8 sets would have been a pain.

On the other end where pad mounts sitting on vaults so plenty of room to crisscross the cables to the lugs.

there is no right or wrong, these are preferences and judgement
as long as code compliant doesn't matter

That was pretty much my point to Phil. :)
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Roger...

Because the phases are separated there is a greater impact of inductivity caused by phase-separation, thereby increasing the "effective resistance"! The result is higher losses than when the 3-phase conductors are bundled in groups of three (tre-foil).

The added "resistance" increase varies as conductor-size increases! For example, up to say #4 AWG (cu), the increase is nil! But for 250 kcmil, the increase is appreciable. If configuration is tre-foil, and operated near rated-current, resistance is r-Ohm/k-ft, but if arranged with separation of say 5-diameters shown in photo (my guesstimate) effective-resistance will increase by 1.05-1.15 x r-Oms/k-ft (an increase of 5-15%!

Phil

Phil, the groups might as well be in one large conduit if they are routed correctly, they are in non ferrous raceways.

Now addressing the grounded conductors being run with each phase in their respective conduits in lieu of their own conduits.

Let's use a hypothetical situation where at a given moment the only current flow is on "A" phase and the grounded conductor. With current division on the grounded conductors the only current flow in the "B" and "C" conduits is on the grounded conductors, why is this better than having the grounded conductors routed in their own conduits?

Roger
 

Ingenieur

Senior Member
Location
Earth
But look at how much easier it was to get all conductors of same phase the same length by doing it that way. Now you have to justify cost of that vs, being able to go with smaller conductors if you put all three phases and neutral in each raceway, if it is about a wash then what was pictured will likely win out.

That is why the length is important
what ampacity?

less wires = less terminations
and cutting is cutting
although this easier to get a 'clean' looking result
but with a skilled electrician the labor difference is small imo
 

Ingenieur

Senior Member
Location
Earth
Assume 2500 A and use 8 sets
no neutral ignore egc
if grouped by phase 3 runs x 8 conductors with 30% derating and 20% fill
700 mcm
5600 mcm / lf
3 pvc runs
too lazy to look up the conduit lol

if balanced 6 x 3 no derating
600 mcm
3600 mcm / lf
6 smaller pvc runs

depending on length could be significant
again, an educated judgement based on cost
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
The problem of separation increasing cable losses is exacerbated because the ducts are non-magnetic!

Phil
That still doesn't answer the question.

Using your theory of non ferrous raceways it would be the same problem even if the raceways contained all phases and grounded conductor.

Roger
 

Phil Corso

Senior Member
That still doesn't answer the question.
Using your theory of non ferrous raceways it would be the same problem even if the raceways contained all phases and grounded conductor.
Roger

It has to do with separation between phases. In the case you illustrated the distances between phases are not symmetrical, but instead asymmetrical, hence the problem!

If each group of a three-phase bundle were installed in one conduit, their conductors would be more equidistant, hence effective-resistance in each bundle is minimum! Consider the extreme case, i.e., installing each of the 12 phases in its own conduit!

Phil
 
Last edited:

Phil Corso

Senior Member
I agree. If one obeys the same length rule, it is really hard to get a balanced set installation to not look like a rats nest. I always try real hard and I am never happy with it.

Obviously a key-factor is circuit-length! There is a saving grace, operating-current is seldom rated-current! But, never use it as an excuse in design!

Phil
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
It has to do with separation between phases. In the case you illustrated the distances between phases are not symmetrical, but instead asymmetrical, hence the problem!

If each group of a three-phase bundle were installed in one conduit, their conductors would be more equidistant, hence effective-resistance in each bundle is minimum! Consider the extreme case, i.e., installing each of the 12 phases in its own conduit!

Phil


Phil there is no guarantee that the conductors would lay symmetrical in a conduit and although not practical, given a few hot box benders I could weave 8 raceways like a rope.

The bottom line is, there is no real reason not to do individual phase installations if it is feasible and all the reasons that Ingenieur brought to the table are considered.

Roger
 

Ingenieur

Senior Member
Location
Earth
Inductance is proportional to the log of seperation
So if less than 10 times as much it is moot
even at 100 times only doubles
at an increase of 10 times dist it is ignored

and the equation has multiple factors, some of which do not change, which further reduces the significance of seperation

d is dist between conductors
GMR geometric mean radius is a property of the conductor radius x e^-0.25
 
Last edited:

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
The problem of separation increasing cable losses is exacerbated because the ducts are non-magnetic!

Phil

The code language addresses putting sets of phases plus grounded (not necessarily neutral) together as sets in raceway, and isophase installation with each phase or neutral in its own conduit(s).
It does not specifically mention mixing phase and neutral as a variation on isophase.

If you have a balanced load, putting returns in one conduit or distributing them across all phase conduits will have exactly the same inductance. (Nothing to cancel).
If you look at a single phase fault to ground or neutral, then putting full sized neutrals in each phase conduit would be ideal. Splitting the neutrals evenly across the phase conduits less helpful and might lead to a (momentary) factor of three or even ten overload of some neutrals.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The problem of separation increasing cable losses is exacerbated because the ducts are non-magnetic!

Phil
If you tried an isolated phase installation with ferrous raceways, you will have a much bigger problem than increased cable losses.
 

Smart $

Esteemed Member
Location
Ohio
The problem of separation increasing cable losses is exacerbated because the ducts are non-magnetic!

Phil

If you tried an isolated phase installation with ferrous raceways, you will have a much bigger problem than increased cable losses.
Additionally, Chapter 9, Table 9 indicates inductance is greater using steel conduit. I believe the values are derived from balanced-current circuits within the conduit.
 

Ingenieur

Senior Member
Location
Earth
This makes little sense. In fact the opposite is the case and is a cogent reason for grouping phases.

Absurd

isophase is probably less than 5% of all installations if that
the required derating and oversized cnd make it less cost effective

using words like 'cogent' does not impress nor make your case any more valid
 