35 years
all heavy commercial/industrial
oil/gas
defense infrastructure
bio/pharma
manufacturing
mining
IBEW member for my first 4 years
most of it field work and design build

As I have proven even the example used in this thread would have been easier using the conventional method
2 less conduit
2 less gounds
6 less conductors
16 less terminations
2 less pulls
absolutely no disadvantage vs isophase, in fact a better more cost effective method

I didnt mean any disrespect, many engineers havent done much hands on. I just was wondering if you have done an installation with 4,5, or 6 conductors in parallel and played the "make it look nice without cutting any off game..." and I was proposing that you may feel differently after trying it.
 

kwired

Electron manager
Location
NE Nebraska
How do you account for using 90C amperage wire rating with 75C equipment lugs?
Nearly all general use conductors used today have 90C insulation on them, nearly all terminals they land on are only rated 60C or 75C. You have to go with the lowest rating of what is connected for minimum allowed size of conductor, but can still use 90C ampacity as a starting point when ampacity adjustments are required - primarily adjustments for number of current carrying conductors in a raceway, or ampacity adjustments for ambient temperature.
 

octavian

Inactive, Email Never Verified
I need help on determing what size wire and how many per phase for 4000 amp run of 480v 3ph between a tranformer and switch gear. I know that 500 is 380. if I multiply that by 10 it is 3800 and by 11 it is 4180. Would that be 10 or 11 sets? And is a set defined as A,B,C,& GRD?

A little late to the game but noticed you didn't mention a neutral. If wired in a delta config no neutral used but should include it anyway for future use. If transformer is POCO equipment connecting a service a ground is not normally run nor wanted.
 