I think the reason you dont see more isophase installations where they would be permitted are:
1. most electricians dont know about his method or have some irrational fear of it
2. most electricians dont follow the same conductor length rule for parallel runs so there is significantly less advantage to isophasing
3. many people dont seek to improve or find better ways
As someone who has wrested with polyphase grouping, keeps conductors the same length, and tries real hard to make it look neat, I fully agree. Some may think it is "no big deal" to have the conduits a little further apart, but the hassle increases rapidy. Say two of the pipes are 18 inches apart. That is 18 inches of conductor that has to go somewhere. I would probably isophase each and every time I had the opportunity. So you can only have 3 conductors per conduit without derating, that probably bumps you down to a smaller pipe size.
1. most electricians dont know about his method or have some irrational fear of it
2. most electricians dont follow the same conductor length rule for parallel runs so there is significantly less advantage to isophasing
3. many people dont seek to improve or find better ways
The 3 lugs will typically be arranged in a line.
With isophase, each lug will have 9 conductors going to just 3 different conduits, and those conduits carry nothing else. You can arrange those conduits so that one is under the lug, the others are neighboring and spread perpendicular to the spread of the lugs. The variation in lug to conduit distance is low, and it is not much trouble to keep the conductors all the same length. The layout of conduits is a separate issue for each lug, no interference.
With mixed phase, each lug will have 9 conductors, 1 going to each of the 9 different conduit. The spread of those 9 conduits will be much greater. Also, at most one lug can be centered over the centroid of the conduit pattern; for the other lugs, the spread of distances from lug to conduit will be quite a bit higher. It will be harder to keep all the conductors the same length.
As someone who has wrested with polyphase grouping, keeps conductors the same length, and tries real hard to make it look neat, I fully agree. Some may think it is "no big deal" to have the conduits a little further apart, but the hassle increases rapidy. Say two of the pipes are 18 inches apart. That is 18 inches of conductor that has to go somewhere. I would probably isophase each and every time I had the opportunity. So you can only have 3 conductors per conduit without derating, that probably bumps you down to a smaller pipe size.