400A service with (2) 200A panels

RdmanElect

Member
Location
Poughkeepsie NY
Occupation
Electrical Contractor
I have a 400A service rated ats feeding (2) 200A panels in the basement. Just want to verify it meets code. I'm using parallel conductors
b90ef17610770ee44510e304941293ce.jpg
968c35ce4395162435e5a9972a7dab04.jpg


Sent from my Pixel 7 using Tapatalk
 

RdmanElect

Member
Location
Poughkeepsie NY
Occupation
Electrical Contractor
2017 NEC 312.2, last sentence: "For enclosures in wet locations, raceways or cables entering above the level of uninsulated live parts shall use fittings listed for wet locations."

Cheers, Wayne
PVC connectors aren't rated for wet locations?

Sent from my Pixel 7 using Tapatalk
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
PVC connectors aren't rated for wet locations?

Sent from my Pixel 7 using Tapatalk
The connection between the connector and the enclosure is not without a sealing washer. At least one manufacturer of PVC male adapters has a sealing washer for there connectors that will give it the required rating to be installed above the live parts.
 

RdmanElect

Member
Location
Poughkeepsie NY
Occupation
Electrical Contractor
The connection between the connector and the enclosure is not without a sealing washer. At least one manufacturer of PVC male adapters has a sealing washer for there connectors that will give it the required rating to be installed above the live parts.
Thank you

Sent from my Pixel 7 using Tapatalk
 