jaggedben
Senior Member
- Location
- Northern California
- Occupation
- Solar and Energy Storage Installer
Yes a sealing *washer* on the outside works fine but a sealing *locknut* on the outside takes up a lot more thread space. As I said YMMV. I'm lucky if I get a full 1/2" of thread on my connectors. The point was that putting a sealing locknut on the inside meets code.Other than maybe a PVC box with thicker walls, I've never encountered an enclosure where a terminal adapter, or male adapter, as some call them, didn't come through enough to put a locknut and bushing on and have room after that. There is over a half inch of threads there after the locknut is on. Putting a sealing washer on the outside wouldn't lesson the thread exposure enough to prevent a locknut and bushing.