I am located in a state that has adopted UEC however it is only licensed and inspected by cities that require it. Hence the problem. I have seen older oil wells that have a 3 wire grounded phase 480 to ground reference on two legs and 0 on the other phase usually B phase.
I have no fourth wire coming as a low impedance circuit to the main disconnect at the utility pole hence the ECG is only tied to the grounding rods.
I have talked with inspectors in the cities, power companies and other electricians and don't really get any feedback on this subject. I ve milled through NEC and feel 4th wire or changing to single phase is the only real option here to protect myself and others. Any feedback on this would be extremely helpful!
I have no fourth wire coming as a low impedance circuit to the main disconnect at the utility pole hence the ECG is only tied to the grounding rods.
I have talked with inspectors in the cities, power companies and other electricians and don't really get any feedback on this subject. I ve milled through NEC and feel 4th wire or changing to single phase is the only real option here to protect myself and others. Any feedback on this would be extremely helpful!