Data plate states 208y/120 60 Hz but the breaker says "Rated frequency 50 Hz". What would happen to this breaker at 60 Hz?
Thanks
Thanks
If it has electronic trips, it may not function properly, it is something only the breaker mfr can answer. If it is a basic thermal-mag breaker, not an issue from an electrical standpoint. But showing only a 50Hz label would be an indicator that the breaker may not be UL listed which, if the generator is going to be hard wired and inspected, might become problematic.Data plate states 208y/120 60 Hz but the breaker says "Rated frequency 50 Hz". What would happen to this breaker at 60 Hz?
Thanks
Probably like all of the US breakers with similar 'push to test' buttons (usually found on >150A frames). The button physically moves the same trip mechanism parts as either the thermal element or the magnetic element. This button typically operate more internal parts than does the on-off mechanical handle.... but how does that trip button work?
Probably like all of the US breakers with similar 'push to test' buttons (usually found on >150A frames). The button physically moves the same trip mechanism parts as either the thermal element or the magnetic element. This button typically operate more internal parts than does the on-off mechanical handle.
But showing only a 50Hz label would be an indicator that the breaker may not be UL listed which, if the generator is going to be hard wired and inspected, might become problematic.
In terms of arc interruption, its job should be easier at 60Hz.
But clearing times specified in fractions of a cycle instead of milliseconds would come out wrong.
The problem I would have with it is that it does not have an AIC rating meaningful in the US.
Its a genny, AIC is not determined by the breaker.
AIC of the genny is determined by some internal workings, I have the doc's here somewhere and should find them as the inspector on this job is super sharp.
How do the CE Ics and Icu values listed compare to the US AIC?http://www.delixi.com/english/aboutdlx/pdf/circuit/CDM1.pdf
The literature says it is suitable for 50/60 Hz.
The problem I would have with it is that it does not have an AIC rating meaningful in the US.
They do not. However, it would be possible to calculate the generator SCA using IEC methodologies.How do the CE Ics and Icu values listed compare to the US AIC?
Its a genny, AIC is not determined by the breaker.
The generator puts out SCA (Short Circuit Amps) during a fault condition, just like the utility does.
The breaker AIC (Amps Interrupting Capacity) is determined by the breaker manufacturer.
The breaker AIC must be greater than the SCA it is connected to.