stickboy1375
Senior Member
- Location
- Litchfield, CT
Dennis Alwon said:Hey I like doing it that way.--- 4 ways also
(me too) Shhhhh....
Dennis Alwon said:Hey I like doing it that way.--- 4 ways also
Bulldog1401 said:As for the 25 ohm thing, if it does not count, why is it mentioned at all? And if so, if the first rod does not achieve it, and the second does not have to achieve it, why drive the second? .
Read the commentary on 250.53(D)(2). I know that commentary is not enforceable, but the message is telling us to achieve 25 ohms to ground
Bulldog1401 said:but the message is telling us to achieve 25 ohms to ground.
It doesn't go on to say "until 25 ohms or less can be measured".If 25 ohms or less of earth resistance cannot be achieved with one rod, pipe, or plate, another electrode (other than the metal piping that is being supplemented) must be provided.
Author’s Comment:
No more than two ground rods are required, even if the total resistance of the two parallel ground rods exceeds 25 ohms.
larry It's more accurate to say that the balance of the electricity flows because it found another way said:unless[/I] that path is able to reduce the voltage across your contact points.
Bulldog1401 said:Please find this exact verbage in the NEC and Quote it to me.
Bulldog1401 said:If you are talking about an infinitely sustained sorce of voltage, such as line voltage, your application of the basic rules of parallel circuits hold water. But lightning, spikes, and other anomolies 9what we are actually talking about here) are more like capacitor.. short finite bursts of energy that causes current to flow. the largest part of the energy will be dissapated on the least resistive path. Lesser ammounts will be dissapated on hire resistance paths. Until the energy is spent, and the potential difference is zero. As this change occurs, the properties you mentioned.. current and voltage are variable, but to a degree, the resistance orf the circuit remains unchanged.
look at a lightning struck tree. clearly the whole tree was struck at once. clearly the energy took a narrow path of least resistance, causing the burnt spot. the whole tree and bark was not burnt, just the path that the energy traveled through to ground. With your theory, you would not be able to tell which path the energy took.
I know I would!petersonra said:. . . you could have zero ohms resistance to ground and it would probably react no differently when hit by lightning than if it were 500 Ohms of resistance.
roger said:As George said, I already did. Click the link he provided.
petersonra said:Lightning is a high speed phenomenon. My guess is that the resistance in the circuits struck by lightning is not a significant factor, when compared to the inductive reactance. IOW, you could have zero ohms resistance to ground and it would probably react no differently when hit by lightning than if it were 500 Ohms of resistance.
Nor does it say the opposite. If your interpretation was the right one, it would say " ... one or more ... " and/or " ... until reaching 25 ohms."Bulldog1401 said:It does not now nor has it ever said what ever the ohms reading is at that time is good enough.
roger said:If you want the exercise, drive as many as you want, the rest will drive the code required two and go home.
Roger
It does not say that in so many words, but it does say that.The code says 25 OHMS. It then says that a water pipe ground shall be supplimented by another electrode. If that does not measure 25 ohms, then you must drive one more rod. It does not now nor has it ever said what ever the ohms reading is at that time is good enough.
Don250.56 Resistance of Rod, Pipe, and Plate Electrodes
A single electrode consisting of a rod, pipe, or plate that does not have a resistance to ground of 25 ohms or less shall be augmented by one additional electrode of any of the types specified by 250.52(A)(2) through (A)(7). Where multiple rod, pipe, or plate electrodes are installed to meet the requirements of this section, they shall not be less than 1.8 m (6 ft) apart.
Bulldog1401 said:The goal is not the number. It is not the number so that people dont try to drive an excesive number of rods until they get it down to 25 ohms. It is so that the rods you do drive are good ones.
Thanks again.
So are 200 amps, 360 degrees, 480 volts, and 50 feet. But they only apply where they apply. You can't merely see a figure or value, such as 25 ohms, and say that it applies blindly to everything in the same paragraph, or even article.Bulldog1401 said:have challenged you to find your exact supporting verbage in the code and as of this point you have not. Which means you are standing on an interpetation, not a fact. It does not matter if the majority carries the same interpetation or not. Facts count, and it is a fact that 25 OHMs is spelled out in the code.