We are starting a residential remodel tomorrow. Homeowner needs a 50 amp range circuit to an island. I’d like to run NM-B wire (romex) from the panel that’s on the opposite end of the house to the island. Homeowner is going to channel the concrete to the nearest framed wall. This means my NMB wire would be in a 1” conduit From the framed wall , in concrete 3” To the island.
I know I’m not supposed to have romex in a conduit especially if I go below the concrete into the soil because it’s a wet location.
I don’t want to pipe all the way back from the Island to the panel and use THWN.
Or
I doubt I’ll be able to get #6-3 MC at supply house. (MC is permissible under ground)
Or
I don’t want to run an NM-B from the panel and transition to conduit & THWN wire to go to the island. I would hate to have a splice point in my range circuit.
Hopefully this inspector will let me run the NMB wire in conduit approximately 10 feet from the framed wall to the island. If I keep the pvc 1” pipe in the concrete I should be OK.
But if I hit the soil with the conduit & NMB it would be considered a wet location and I might fail the inspection.
Any thoughts?
Sent from my iPhone using Tapatalk
I know I’m not supposed to have romex in a conduit especially if I go below the concrete into the soil because it’s a wet location.
I don’t want to pipe all the way back from the Island to the panel and use THWN.
Or
I doubt I’ll be able to get #6-3 MC at supply house. (MC is permissible under ground)
Or
I don’t want to run an NM-B from the panel and transition to conduit & THWN wire to go to the island. I would hate to have a splice point in my range circuit.
Hopefully this inspector will let me run the NMB wire in conduit approximately 10 feet from the framed wall to the island. If I keep the pvc 1” pipe in the concrete I should be OK.
But if I hit the soil with the conduit & NMB it would be considered a wet location and I might fail the inspection.
Any thoughts?