Whats the def for "Locations, Wet" in the NEC ver in play here?
Some slabs may not be in direct contact with earth, so I say here....... it depends.
But sure, just use wet rated wire, sleeve it, home run it, done.
I agree here. The Art 100 definition on "Location Wet" reads
Installations underground or in concrete slabs or masonry in direct contact with earth; in locations subject to saturation with water or other liquids, such as vehicle washing areas; and in unprotected locations exposed to weather.
The only thing that applies here is the SLAB part. There is no getting around its in a slab. It may not be in contact with earth if there is foam insulation under the slab??? The rest does not apply because this will be the kitchen floor.
If the slab had a channel cut in it for the conduit to run through, and then that channel was filled with epoxy would it still be in a slab? No. The environment would still be the same. SO I agree that the code is clear that its considered "Wet Location" but I also agree that there should be an exception here that considers a potentially isolated slab under a kitchen floor "Dry".