This was way back in I can't remember the code cycle,(probably at least twenty years ago) but if you went by Table 9, the calculations would prohibit 3 #6 and one #10, but if you went by annex C, 4 #6 were allowed.
Just ran the calcs in the 2011 edition, and it will work now as it has for a while, but......since conduit area is now listed for individul types, 4 # 6 thhn will not fit in a 3/4" schedule 80 pvc or ENT (smurf pipe) and just barely under on schedule 40 pvc. It could have been a screw up in that old edition, as there have occasionally been a few over the years.
Yes, I believe that those tables did contain some errors over the years. However, the stuff is Annex C is for informational purposes only. Saying that "you could pull 4 #6 thhn in a 3/4" conduit, but could not pull 3 #6 and a #10 in a 3/4" conduit because of a different table you had to use" was never really correct for the same conduit type even if it said so in one of the Annex C tables. You have always been required to calculate fill by doing the calculation.