Meternerd:
I share a 50 kVA transformer with one neighbor and two street lights as the load. This transformer was new several years ago because the original 45 year old transformer was leaking oil.
When the voltage waveforms were taken the neighbors were out of town. I believe our substation is a wye source. But our loading is effectively delta, and several homes have open delta loading. Our transformers are bridged line to line and there is no neutral on the poles.
I believe this is a system wide voltage distortion. At some time I will look at voltage on a different substation.
SG-1:
Was your waveform taken at home or at your lab? Does your scope have the ability to average the signal, thus reducing noise and improving the apparent resolution. I have used various average counts in the above images. Not less than 2 and I don't believe more than 64.
.
Meternerd:
I share a 50 kVA transformer with one neighbor and two street lights as the load. This transformer was new several years ago because the original 45 year old transformer was leaking oil.
When the voltage waveforms were taken the neighbors were out of town. I believe our substation is a wye source. But our loading is effectively delta, and several homes have open delta loading. Our transformers are bridged line to line and there is no neutral on the poles.
I believe this is a system wide voltage distortion. At some time I will look at voltage on a different substation.
SG-1:
Was your waveform taken at home or at your lab? Does your scope have the ability to average the signal, thus reducing noise and improving the apparent resolution. I have used various average counts in the above images. Not less than 2 and I don't believe more than 64.
.