Just like a 460V motor on a 480V supply.Yeah totally. I wonder how a 600V boost transformer and a 575V single phase pump would pencil out.
Yeah totally. I wonder how a 600V boost transformer and a 575V single phase pump would pencil out.
Is there a significant amount of outflow from this lake? Maybe an all-mechanical, non-electric solution is the answer:... Why transmit all the power 2,000 feet when you might only need 1/4 of the power down at the bottom, and the rest right next to the storage tank?
Because you need to pump it 2000 feet through what size pipe?...
Why transmit all the power 2,000 feet when you might only need 1/4 of the power down at the bottom, and the rest right next to the storage tank?
I forgot what they were @ 67 posts.Should someone go to AHJ and report the findings of the original poster ?
I forgot what they were @ 67 posts.
Ahj don’t care lol they allow it all the time. I agree I should push for some law and tell them I’ll fix it for them lol
Ahj don’t care lol they allow it all the time. I agree I should push for some law and tell them I’ll fix it for them lol
Yeah but right now the pump is doing all the work to get the water to the tank, plus supplying the utilization pressure.Because you need to pump it 2000 feet through what size pipe?
IMHO using GFCI protection on this is a bad idea. The run is so long that nuisance tripping is very very likely.
I strongly agree with the OP's goal of an installation which is safe for people swimming in the lake.
I wonder if an ungrounded system would make the most sense safety wise. In other words use an isolation transformer rather than a boost transformer, with secondary not bonded to primary ground.
I don't think code would permit this, but is it potentially safer, and could the AHJ be convinced of this.
Or could the system be wired with an EGC bonded to the transformer neutral, but not connected to the mains neutral. One of the safety issues in lakes is elevated potential on various ground/ neutral conductors.
Jon
We have a very large lake in Georgia (Lanier) that has several volts on it from everything from improperly installed docks, to failing poco underground lines. The Corp of Engineers is well aware of it."If I said well that’s my bad it’s on the local lake. My dad has water rights and we lost power. Diver found a Beaver attached to the line. Says there is miles of Unsed wires in the lake and splices all over. I will not let my kids swim there is a death trap".
This is not just a conversation about "Code" anymore. This is a real-life safety issue. I just sent an Email to Mike Holt, explaining a life safety issue on his forum, and what support he will have to protect life and safety. Would you allow your family to go into this lake ?
We have a very large lake in Georgia (Lanier) that has several volts on it from everything from improperly installed docks, to failing poco underground lines. The Corp of Engineers is well aware of it.
None that I am aware of , most homes are on one side of the lake and most of the swimming is done on the other side.Do you know of anyone who has been electrocuted on this lake ?