I am having issues with gfci breakers tripping when installed on 7.5 hp single phase pump motors. if im not mistaken, all single phase swimming pool pump circuits regardless of voltage or amperage must be GFCI protected. so when we are faced with a 7.5 hp single phase, 230 volt pump, we are installing a 60 amp, 2 pole GFCI breaker. wiring is simple enough, two ungrounded conductors on breaker go to motor, no load neutral, and pig tail neutral from breaker goes to neutral bar of panel. upon start up, 3 out 3 pumps we have installed these on trip immediately. two of the pumps are the same model. all three of the breakers are the same manufacturer.
could the issue be start up current imbalance? voltage leakage through capacitors? how do you fix this issue?
your ideas and comments are most welcome and thank you in advance
I am having issues with gfci breakers tripping when installed on 7.5 hp single phase pump motors. if im not mistaken, all single phase swimming pool pump circuits regardless of voltage or amperage must be GFCI protected. so when we are faced with a 7.5 hp single phase, 230 volt pump, we are installing a 60 amp, 2 pole GFCI breaker. wiring is simple enough, two ungrounded conductors on breaker go to motor, no load neutral, and pig tail neutral from breaker goes to neutral bar of panel. upon start up, 3 out 3 pumps we have installed these on trip immediately. two of the pumps are the same model. all three of the breakers are the same manufacturer.