ggunn
- Austin, TX, USA
- Consulting Electrical Engineer - Photovoltaic Systems
First off your building a normal distribution to a sub panel at the load end of a feeder and going strictly by what the code says . The first thing to ask is how many slots does the 100 amp sub panel have.
Is it capable of supplying branch circuits and feeders. The installer says it s just to combine the PV inverters outputs. Ok what side of the PV meter is it on. The inspector needs to make a decision.
Now the main service panel I know what previous codes said. So I say you need to do a source calculation on the main MDP. The installer says on both points where does it say that in the code.
The number of slots in the 100A sub is irrelevant; it is compliant because the total ratings of all breakers, supply and load, excluding the OCPD protecting the busbar, does not exceed rating of the panel per 705.12(D)(2)(3)(c).
A PV meter is not required by the NEC. If the AHJ requires one they will decide where it needs to go. That's irrelevant to what I proposed; it would be between the subpanel and the inverter.
The MDP is in violation on two points. The breaker protecting the busbars in the sub must be at the opposite end of the busbar from the main breaker, and the 100A from the inverter must fit within 120% of the busbar rating minus the main breaker rating. There is only 40A headroom in a 200A panel with a 200A breaker.
I have done hundreds of PV projects from a few kW to over a MW under this interpretation of the NEC in at least 10 jurisdictions. Agreement from inspectors on these points has been 100%.