Yes, stand alone systems have a somewhat different definition as quoted already in multiple previous posts. Stand alone systems are not what we are arguing about.
Not true!! :happyno: The next component is not shown! It's just an arrow pointing to an indefinite ending point! :happyyes: That ending point is defined elsewhere in the code as 'the service equipment or another source ...', and there is nothing in the diagram that suggests there can't be other equipment in between.
He's talking about the branch circuit, not feeders and distribution. I'm not going to search the hour long video for the part you're talking about to see if he paraphrased or mispoke. But I would bet you $5 that he would agree with me.
E-mail him if you like. his e-mail is on his website (see bottom of page)
http://brooksolar.com/contactus.html
Ok, I took your advice and did Email Mr Brooks
Dear Mr. Brooks;
I was hoping to gain your insight to help clarify the point of termination for the Inverter Output Circuits for a load side connection point and specifically when that connection point originates in a load side connection at a subpanel. I have included the definition in 690.2 although my contention is really the definition in 705.2
I find the definition for inverter output circuits to be descriptive. The definition seems to simply describe the inverter output circuits under three conditions in 690.2
1. Stand-alone systems inverter to ac panel board (out side the scope of article 705)
2. Inverter to the service equipment. ( to the service equipment neither line side or load side connection point 705.12)
3. Inverter to another electric power production source, such as a utility ( in article 705.12 line side connection point)
Looking at the definition of service equipment intended to constitute the main control and cutoff of the supply and being connected to the load end of service conductors. I find the definition for inverter output circuits to be awkward at best to try and apply it to a load side connection point in article 705.12
I am being told by individuals that I would call experts in this field that the inverter output circuits include all conductors and bussbars from the load side connection point in a subpanel in series with the service disconnect for the utility, to the utility service equipment.
I find that to be awkward, that being the only time the inverter output circuits would be defined as part of load distribution conductors. I also find it awkward to be redefining conductors such as feeders to be inverter output circuit conductors.
I find the definition for inverter output circuits in 705.2 to be missing a description for a load side connection point. I am therefore unsure if this definition as given in 705.2 should be applied to a load side connection point.
I am not a professional graphics designer, I have included some graphics to try and help clarify what I am asking. Any opinion you have on clarifying where the inverter output circuit’s end on a load side connection point would be appreciated.
David