I don't know Articles 690 or 705, but the Article 100 definitions say services always come from the utility, so unless there is some weird redefinition of the term service in Articles 690 or 705, there is no such thing as PV source service equipment.
See the Article 100 definitions of Service Equipment (which you already quoted), Service Conductors, and Service Point. Only a utility can provide a service point, and without a service point there are no service conductors and no service equipment.
Cheers, Wayne
I agree 100 % that the term service means utility service.
"Service. The conductors and equipment for delivering electric energy from the serving utility to the wiring system of the premises served."
690.2
Inverter Output Circuit. Conductors between the inverter and an ac panelboard for stand-alone systems or the conductors between the inverter and the service equipment or another electric power production source, such as a utility, for electrical production and distribution network.
Service Equipment. The necessary equipment, usually consisting of a circuit breaker(s) or switch(es) and fuse(s) and their accessories, connected to the load end of service conductors to a building or other structure, or an otherwise designated area, and intended to constitute the main control and cutoff of the supply.
And I am embarrassed to admit I was reading this as a permissive rule that a building was permitted to be supplied by a Parallel power production system
It’s not a permissive rule to supply a building with a parallel power production source. It’s a permissive rule for an additional utility service for the purpose of supplying a parallel power production system
230.2 Number of Services.
A building or other structure served shall be supplied by only one service unless permitted in 230.2(A) through (D). For the purpose of 230.40, Exception No. 2 only, underground sets of conductors, 1/0 AWG and larger, running to the same location and connected together at their supply end but not connected together at their load end shall be considered to be supplying one service.
(A) Special Conditions. Additional services shall be permitted to supply the following:
(5) Parallel power production systems