- New Jersey
- Journeyman Electrician (retired)
Personally I prefer to keep the 42 circuit limit. I can just see an 80 circuit panel with 50, 60, 70 or 80 two wire cables coming into tho top. Talk about a mess.
I'll bet your panel has rejection features so that you cannot install 40 tandem breakers...of course you could if you use non-CTL breakers.Its the same panel you get in the US. I have one in my basement.
LAYMAN JOE said:I agree! Please dont misunderstand me. 40 tandem breakers is 80 circuits. 40 sp breakers with two wires on it is still only 40 circuits, not 80.
I thought I was clear in stating my opinion that its a play on words by square D (a marketing ploy). They give you 40 spaces, say it can have 80 circuits, and sell it in the US where it would be a violation to have more than 42 circuits.
Why would they advertise a product that would violate NEC? It doesn't make sense. It must be a marketing ploy for the do it yourself home owner. As I said:
Im not the best at clearly communicating through writing, sorry.
infinity said:Personally I prefer to keep the 42 circuit limit. I can just see an 80 circuit panel with 50, 60, 70 or 80 two wire cables coming into tho top. Talk about a mess.![]()
iwire said:I think a 42 can be crowded enough and I work with 21" W x 7" D panel boards, never mind a 14.5" W x 3.5" D Load center.
infinity said:The 14 1/2" X 3 1/2" panel was exactly what I was thinking about.
LAYMAN JOE said:....I thought I was clear in stating my opinion that its a play on words by square D (a marketing ploy). They give you 40 spaces, say it can have 80 circuits, and sell it in the US where it would be a violation to have more than 42 circuits.
Why would they advertise a product that would violate NEC? It doesn't make sense.....
georgestolz said:One thing about it, we would have more room to space out AFCIs
1- AFCI SPACE -2
3- SPACE AFCI -4
5- AFCI SPACE -6
7- SPACE AFCI -8
9- AFCI SPACE -10
11- SPACE AFCI -12
13- AFCI SPACE -14
15- SPACE AFCI -16
17- AFCI SPACE -18
19- SPACE AFCI -20
And then there comes the question, will the manufacturers acknowledge on some level that their AFCIs are too warm to snuggle up to each other, and start making 80/160 panelboards?iwire said:There are no tandem AFCIs, so just allowing a 40/80 panel does not seem to solve any problem.
iwire said:Sean it looks like under the 2008 NEC almost all circuits in dwelling units will be required to have AFCI protection.
AFCI breakers run hot and at least one AFCI maker recommends that AFCIs are not located side by side.
An 80 circuit panel may be needed so you can space the AFCIs out leaving spaces between them.
I do not believe it is a coincidence that an AFCI manufacturer is behind the proposal to allow 80 circuit panels.
Pierre C Belarge said:I think that some areas of the home will not require the AFCI, but many will.
(B) Dwelling Units. All 120-volt, single phase, 15- and
20-ampere branch circuits installed in dwelling units shall
be protected by a listed arc-fault circuit interrupter, combination
type installed to provide protection of the branch
circuit. [ROP 2–105, 2–142, 2–111]
Pierre C Belarge said:With the advent of the newer type AFCI (combination type) the running temp for the electronics of the AFCI will become somewhat lower.
About the circuit allowance for panel enclosure/panelboards change. The manufacturers do not want anymore liability than in the past. With that said, there will be limitations as to the number of circuits per panelboard, but those limitations will not be directed by the NEC other than 110.3(B).