83 % rule apply with feeder taps?

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Kind of similar to my earlier mentioned multi family situation where each is supplied via a tap. I think it is ok. Taps can't utilize the next size up rule and this is mentioned in 240.21(B).

conductors supplying a dwelling get a special adjustment so to speak with the 83% which effectively makes the ampacity of 4/0 aluminum 216 amps - 200 amp OCPD does not exceed the ampacity of the conductor.
I don't see the 83% rule as changing the conductor ampacity...just a permission to protect the conductor with an OCPD that has a rating higher than the ampacity of the conductor...just like 240.4(B) does not change the ampacity, but only permits the conductor to have overcurrent protection higher than its rated ampacity. The words below tell me that the 83% rule does not actually change the conductor ampacity.
shall be permitted to have an ampacity not less than 83 percent of the service rating
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
I don't see the 83% rule as changing the conductor ampacity...just a permission to protect the conductor with an OCPD that has a rating higher than the ampacity of the conductor...just like 240.4(B) does not change the ampacity, but only permits the conductor to have overcurrent protection higher than its rated ampacity. The words below tell me that the 83% rule does not actually change the conductor ampacity.
I agree. Under the old 310.15(B)(7) table a few cycles back it was much more ambiguous what the actual 'ampacity' of the conductors was. But the way 310.12 is worded nowadays makes it as Don says.
 

Sparky38

Member
Location
Plant City
Occupation
Electrical Inspector
I agree. Under the old 310.15(B)(7) table a few cycles back it was much more ambiguous what the actual 'ampacity' of the conductors was. But the way 310.12 is worded nowadays makes it as Don says.
You cannot use the 83% rule on the feeders because neither feeder by itself supplies the whole dwelling and they are smaller than the service conductors. That's the end of that discussion, taps or not.

Now you also have taps. They can't use the next size up rule so with 4/0 Al they can't be on more than a 175A breaker.

If, say, you instead had a 400A distribution panel with a main breaker and two 200A breakers, 4/0 Al would be okay if the calculated loads were 180A or less.

OP Here are we agreeing that this post is correct? And also that SER Cable cannot be run through the wall and attic (tap conductors need a raceway)
 

kwired

Electron manager
Location
NE Nebraska
I don't see the 83% rule as changing the conductor ampacity...just a permission to protect the conductor with an OCPD that has a rating higher than the ampacity of the conductor...just like 240.4(B) does not change the ampacity, but only permits the conductor to have overcurrent protection higher than its rated ampacity. The words below tell me that the 83% rule does not actually change the conductor ampacity.
I really don't know what code intends. Seems to not be absolutely clear whether you could use that 310.15(B)(7) for a feeder tap. You certainly can supply exact same load with a service conductor sized via this method though. Is one that much more of a hazard than the other?
 

Sparky38

Member
Location
Plant City
Occupation
Electrical Inspector
I really don't know what code intends. Seems to not be absolutely clear whether you could use that 310.15(B)(7) for a feeder tap. You certainly can supply exact same load with a service conductor sized via this method though. Is one that much more of a hazard than the other?
I just figured that since they don’t let you go up to next standard breaker size that the 83% would not apply either, I believe they should add this into code. 83% not permitted on taps where it’s says cannot round up to next size standard breaker for taps. To cut down on the confusion. Just trying to figure out right from wrong.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
I just figured that since they don’t let you go up to next standard breaker size that the 83% would not apply either, I believe they should add this into code. 83% not permitted on taps where it’s says cannot round up to next size standard breaker for taps. To cut down on the confusion. Just trying to figure out right from wrong.
I'm struggling to think of a possible way that a tap would ever qualify for the 83% rule in the first place. If it's protected by the service disconnect OCPD it's not a tap. If it's small enough to be a tap then it doesn't qaulify for the 83% rule for one or more reasons. So it's a moot question.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
I'm struggling to think of a possible way that a tap would ever qualify for the 83% rule in the first place.
As in:

400A service OCPD for multiple dwelling units/buildings -- 200A ampacity feeder tap, main feeder for a dwelling unit -- 200A OCPD -- 166A ampacity feeder, 200A rating main feeder for a dwelling unit -- 200A MLO distribution panelboard.

?

Cheers, Wayne
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
As in:

400A service OCPD for multiple dwelling units/buildings -- 200A ampacity feeder tap, main feeder for a dwelling unit -- 200A OCPD -- 166A ampacity feeder, 200A rating main feeder for a dwelling unit -- 200A MLO distribution panelboard.

?

Cheers, Wayne
Ah, okay. Multiple dwelling units on a service. I think that's the only way.

The way I would put it is that 310.12 applies but 240.21 overrides it.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Can you expand on that I'm not seeing it, that you can't use the 83% rule for a feeder that carries the entire load of a dwelling unit if it is rated smaller than the service.
I was thinking of a service that only supplies a single dwelling unit, and is not oversized. You're correct it's not true in every last case. So much for being precise.
 
I'm struggling to think of a possible way that a tap would ever qualify for the 83% rule in the first place. If it's protected by the service disconnect OCPD it's not a tap. If it's small enough to be a tap then it doesn't qaulify for the 83% rule for one or more reasons. So it's a moot question.
As in:

400A service OCPD for multiple dwelling units/buildings -- 200A ampacity feeder tap, main feeder for a dwelling unit -- 200A OCPD -- 166A ampacity feeder, 200A rating main feeder for a dwelling unit -- 200A MLO distribution panelboard.

?

Cheers, Wayne
Why not just a 200A service disconnect, 100A conductors connected to the load terminals of the 200A device, to 100A MB panel, all serving a single dwelling unit?
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Why not just a 200A service disconnect, 100A conductors connected to the load terminals of the 200A device, to 100A MB panel, all serving a single dwelling unit?
Only that that would be weird and I've never seen such a thing. Pardon my lack of imagination.
Regardless, whatever unusual scenario you come up with, 240.21 just overrides 310.12.
 

Sparky38

Member
Location
Plant City
Occupation
Electrical Inspector
Only that that would be weird and I've never seen such a thing. Pardon my lack of imagination.
Regardless, whatever unusual scenario you come up with, 240.21 just overrides 310.12.
As in:

400A service OCPD for multiple dwelling units/buildings -- 200A ampacity feeder tap, main feeder for a dwelling unit -- 200A OCPD -- 166A ampacity feeder, 200A rating main feeder for a dwelling unit -- 200A MLO distribution panelboard.

?

Cheers, Wayne
This service I mentioned is controversial depending on how you interpret the code book. Codes not clear in this particular scenario. My interpretation of the code is 83% is ok from meter to 400 breaker disco, Then the feeder conductors from disco to the 2 200 amp panels with main breakers located in garage on interior wall should be sized for 200 amps (250 al or 3/0 cu) installed within a raceway. I failed this site and was overridden by a super, contractor ran 2 sets of 4/0 al ser cable from disco to panels total length 25’ up walls and about 10’ through the attic without a raceway. I did not agree with this install.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
This service I mentioned is controversial depending on how you interpret the code book. Codes not clear in this particular scenario. My interpretation of the code is 83% is ok from meter to 400 breaker disco, Then the feeder conductors from disco to the 2 200 amp panels with main breakers located in garage on interior wall should be sized for 200 amps (250 al or 3/0 cu) installed within a raceway. I failed this site and was overridden by a super, contractor ran 2 sets of 4/0 al ser cable from disco to panels total length 25’ up walls and about 10’ through the attic without a raceway. I did not agree with this install.

I would talk to my superior and explain that not only is the install non-compliant but dangerous as well. I have no problem with the 4/0 Al in parallel but it must be in a raceway or cable.
 

Sparky38

Member
Location
Plant City
Occupation
Electrical Inspector
I would talk to my superior and explain that not only is the install non-compliant but dangerous as well. I have no problem with the 4/0 Al in parallel but it must be in a raceway or cable.
Thanks, So you would allow the 83% on this install on the feeders even though the 200 amp breakers are not at the point of supply (tap conductors)
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I just read the op again and I didn't think you could run seu cable in parallel.

(3) The tap conductors are protected from physical damage
by being enclosed in an approved raceway or by other
approved means.
 

Sparky38

Member
Location
Plant City
Occupation
Electrical Inspector
I just read the op again and I didn't think you could run seu cable in parallel.
Well I wouldn’t call it parallel, Because each cable runs to separate 200 amp panels. So it’s a 400 amp main breaker disco, with 2 4/0 al ser cables under each lug on load side of breaker going to 2 separate panels
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Well I wouldn’t call it parallel, Because each cable runs to separate 200 amp panels. So it’s a 400 amp main breaker disco, with 2 4/0 al ser cables under each lug on load side of breaker going to 2 separate panels
Yes but how large is the equipment grounding conductor in the 4/0 ser? It must be large enough for the 400 amp breaker which would be at least #1 al.

Well maybe I am wrong again.... It is a tap but not parallel so I am not certain the equipment grounding conductor needs to be any larger than a #6 cu or 4 al.
 

Sparky38

Member
Location
Plant City
Occupation
Electrical Inspector
Yes but how large is the equipment grounding conductor in the 4/0 ser? It must be large enough for the 400 amp breaker which would be at least #1 al.

Well maybe I am wrong again.... It is a tap but not parallel so I am not certain the equipment grounding conductor needs to be any larger than a #6 cu or 4 al.
4/0 4/0 4/0 2/0 Ser cable, So equipment ground is good, Each cable does not supply the whole load, and per 240.21 you can’t cannot go up to next size breaker size. So in my opinion I think that they should use 175 amp mains Inside Panels or install 250 al in a raceway to comply
 