This service I mentioned is controversial depending on how you interpret the code book. Codes not clear in this particular scenario. My interpretation of the code is 83% is ok from meter to 400 breaker disco, Then the feeder conductors from disco to the 2 200 amp panels with main breakers located in garage on interior wall should be sized for 200 amps (250 al or 3/0 cu) installed within a raceway. I failed this site and was overridden by a super, contractor ran 2 sets of 4/0 al ser cable from disco to panels total length 25’ up walls and about 10’ through the attic without a raceway. I did not agree with this install.