As Jim just mentioned, if you remove that Main Bonding Jumper in the PV line side disconnect and make no other changes, then the EGC system originating there will have no intentional fault clearing path. I.e. if you don't have an inadvertent interconnection of the two EGC systems, then on the PV wiring, a line to EGC fault would not clear but simply energize all the bonded metal parts. If you subsequently touch those bonded metal parts and the earth, or the EGC system of the primary service disconnect, you would get shocked or electrocuted.
Cheers, Wayne