Well I tske thst bsck. If you have a separate service entrsnce panel for solar with a separate utility connection in probably a dual- metering system then neutral would be bonded to ground in that second panel BUT there must then be no electrical connections at all between the L1,L2,N or ground or the solar system and the house wiring. Effectivley you have to treat it as if they were sepatate houses!
IMHO this is one of those situations where code and physics don't align well.
In general code requires that there be one (and only one) connection between the 'grounded circuit conductor' (the 'neutral') and 'non-current carrying exposed metal' (everything connected to or used as the EGC, including metallic piping and conduit, metal equipment frames, etc). But this requirement is 'per service', and code doesn't do a good job dealing with multiple services.
This is a known problem in residential situations with a shared underground metallic water pipe system, where you have a ground-neutral bond in each residence, and each residence has a GEC connection to the water pipe. Significant neutral current can flow on the water pipes, and in addition to stray magnetic fields caused by this, plumbers have been electrocuted when working on underground water pipes.
This is also a possible problem when you have multiple services on one building, or in the very common situation of a 400A residential service built with a pair of 200A panels; you have a ground-neutral bond in _each_ service disconnect. Usually, however, the parallel path issue when you have multiple services on one building is confined to the local region of the service equipment. Yes, you have a parallel path for neutral currents, but with a shared neutral conductor in the service drop, the voltage difference between the two neutral bond points is very small, and since both are physically in the same location any parallel neutral currents driven by this small voltage difference are confined to the shared GEC between the two bond points.
The calculation in post #45 points to the relative magnitude of any 'parallel path' current induced between the service equipment at the service equipment vs 'parallel path' current going down one EGC and returning on another EGC for the other service. Obviously that example was pulling numbers out of the air, but the general feel is correct: if any current is flowing on this parallel path, far more is flowing on the fat GEC conductors near the service(s) than down branch circuit EGCs.
To the OP:
1) If I found high current flowing on an EGC, I would not spend time chasing parallel paths caused by ground/neutral bonding at the service. I would be looking for any ground-neutral connections at a distance from the service equipment. The multiple ground/neutral bonds in a single service entrance are IMHO slightly problematic but are code legal and not likely to be the source of hundreds of ma of current on a branch circuit EGC.
2) One possible source of currents on an EGC are ground referenced filters and surge protective devices. These are often connected between line and 'ground' (EGC), and can inject current into the EGC system.
3) Another possible source of currents on an EGC are connections to external ground electrodes. This is not code prohibited, but if there is any current flowing through the soil from external sources (say utility MGN design or a line-earth fault at an adjacent customer), then ground electrodes can act to carry current in from the soil at one electrode, pass it through the EGC system, and have it exit another ground electrode. Code permits 'supplemental' grounding electrodes to be connected to the EGC, rather than requiring a solid connection via the GEC. Is it possible that the solar installation included its own ground rod? Could the solar ground be connected to a non-bonded unintentional connection such as a cast iron sewer waste stack?
4) I cannot condone a non-electrician making measurements inside the electrical equipment. This is not a DIY forum. However if you are chasing currents injected into the EGC system to try to eliminate stray magnetic fields, keep in mind that you are looking for _net current_ on each circuit path. You really should be putting your clamp around the _entire_ circuit, conduit and all. Any current that is balanced by nearby current in the opposite direction nets to zero and doesn't result in a widely spreading magnetic field. You will see high fields between the conductors of a circuit, but not any significant distance from the circuit. So take your current clamp around the entire MC cable from the PV system. Is there larger _net_ current on that cable?
5) I have a close friend who has electromagnetic sensitivity, and have seen enough to believe that there is something there. My personal _hunch_ is that it is psychosomatically mediated. To be very clear, I am _not_ trying to dismiss you by saying 'it is all in your head', rather my hunch is that someone _perceives_ AC E or B fields, and that sensation triggers further responses that are called electromagnetic sensitivity. The reason I believe that this is important is because if the issue is mediated perception, then any other sensation which triggers the same mediation will be 'felt' as an electromagnetic problem.
I am personally very sensitive to the high frequency _audio_ hiss that some switching power supplies create. If my phone is plugged into the wrong sort of charger near my bed, then it interferes with my sleep. This is nearly white noise that is very difficult to discern and disambiguate unless you put your ear right up to the power supply, but I find that it _really_ bugs me.
I bring this point up because in my hunch you are feeling _something_, but it right at the edge of perception, and hard to pin down. It is very easy to keep chasing one possible source of this annoying sensation, and ignore chasing other more fixable sources. You might be responding to the acoustic noise of the PV inverter, not to the electromagnetic fields of the system.
Good luck
Jon