jaggedben
Senior Member
- Location
- Northern California
- Occupation
- Solar and Energy Storage Installer
The MC conduit would only carry neutral current if it made contact with the neutral (not EGC) of another circuit. I.e some fluke like a screw from a strap holding the MC hit a cable in the wall.What I know is that the EGC from solar" which includes the MC conduit" since it is bonded on PV disconnect is
carrying current from "N" and looping it with the other home EGC wiring.
Have an electrician amp clamp the neutral in the PV disconnect to see if it is actually carrying any current or not.
If the MC conduit is bonded, it would effectively be a neutral wire and if that Neutral wire( conduit) is then touching EGC-home (with less than 1ohm of resistance) then why isn't that viewed as double bonding. Which would be a clear code violation?
Only if the circuit is completed to a neutral wire somewhere else.Bonding just means to bring diverse voltage of two different surfaces into equilibrium with one another. So in this case, so long as that MC conduit remains connected to the PV disconnected with the bonding screw then it acts as a neutral wire.
The only place we have some reason to believe there is a loop is between the main panel and PV disconnect. But we have no reason to believe there's current flowing around that loop. And even if it were, it wouldn't feel any different to you than if it were wired normally, if you can indeed feel any of this stuff.Now we ask the question? If that neutral wire touches a ground wires ( as evidenced by <1ohm) or resistance, whether you wrap around a metal or screw them in doesn't matter very much ( resistance is resistance). You would effectively be creating a second bond no matter how you do it. Why is this not a "clear" code violation?