Jim- a neutral for a feeder does not have to be the same size as the ungrounded conductors just large enough for the load and at least as large as the egc.Yes it would work but no not legal. What happens if the other circuit for what ever reason is not on ? Thats why its a no go. All conductors must be protected. Usually the neutral is protected by the ungrounded conductor being fused