I agree, it's common. I require it to be accessible. I get heavy pushback on that, but it's a pretty clear requirement.
2022 CEC (Based on 2020 NEC)
250.68
(A) Accessibility. All mechanical elements used to terminate
a grounding electrode conductor or bonding jumper to a
grounding electrode shall be accessible.
Exception No. 1: An encased or buried connection to a concrete-
encased, driven, or buried grounding electrode shall not be
required to be accessible.
Exception No. 2: Exothermic or irreversible compression
connections used at terminations, together with the mechanical
means used to attach such terminations to fireproofed structural
metal whether or not the mechanical means is reversible,
shall not be required to be accessible.