OK, let's forget any mention of live work, politics of being self-employed and your mom jokes. (which is not an invitation for your mom or her jokes)
The method of shutting this off, is that 50 year old switch. Would you just walk up and pull that handle?
About 5-6 years ago, I was called to a job in CT to connect generators for the POCO during an outage that they were having.
One building was a 22 story hi-rise residential building with seniors and hookers.
We had to make the connections of the temp cables in two 4000 amp main switches.
I think that were GE switches.
There was a long handle and a little window that would show red or green to indicate the position.
When we operated the switches they made the sound like they switched and the color changed, but we didn't see any of the fingers move. We tried them a couple of times
We found that the grease on all of the moving parts turned to varnish. There were globs of hardened green grease on the moving parts and nothing would move so the switches wouldn't open.
We had to remove all of the main fuses. What a PITA, there were 8 bolts per fuse and we had to remove 6 fuses while everyone was waiting for power.
We notified the FD and the EI of the problem with the main switches and they contacted the owner of the building.
It was a fun scene when the owner arrived and was confronted by the FD and EI.
The owner swore up and down that they test the switches "all the time".
He kept saying that he paid his bill, in very broken engilsh.
From what I saw, those switches haven't moved in 30 years.
I disconnected the generators when the POCO was ready and reinstalled the fuses so they could re-energize the buildings.
I left the problem with the EI, FD and owner to work out.