wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
Yes, of course.So, we have a water pipe electrode with a GEC attached.
Can we tap that GEC and run a bonding jumpers to some ground rods?
Cheers, Wayne
Yes, of course.So, we have a water pipe electrode with a GEC attached.
Can we tap that GEC and run a bonding jumpers to some ground rods?
Yes, of course.
Cheers, Wayne
A Supplemental electrode for a water pipe can connect to just about to anything the service neutral is connected too
A ground rod that is deemed to be present becomes part of the mandate to bond it to the grounding electrode system or connect it to the neutral with a grounding electrode conductor
(2011) 250.64(F) mandates nothing, other than the sentence "The grounding electrode conductor shall be sized for the largest grounding electrode conductor required among all the electrodes connected to it."
Your interpretation would mean that bonding jumpers could only go to busbars, as the only mention of bonding jumpers in 250.64(F) is the allowance to use busbars given in 250.64(F)(3).
Cheers, Wayne
I find it very hard to follow your train of thought. Are you suggesting that the above text says that a bonding jumper has to go from electrode to electrode? I don't see it, connecting the other electrodes via bonding jumpers to the grounding electrode conductor meets the above text. The use of the word "where" in the above text is not locational, it has the meaning "in the situation that"."to any convenient grounding electrode available in the grounding electrode system where the other electrode(s), if any, are connected by bonding jumpers per 250.53(C)."
I've been confused by the weight you have been giving to "required", until the above comment and a couple more that follow. Here in this forum, the views you are reading are solely from the NEC. Electrical Utilities have requirements, yes, however they are local to each Utility and sometimes local to only some offices in a single Utility. The views of this forum's members are given without respect to any local Electric Utility regulations.Here the ground rod is required at every service by the utility,
we do not, since it is a required electrode call it a subliminal electrode since it is required to be in the soil and found to be " present" at every building that is built.
i did not know we where discussing a supplemental grounding electrode
This exchange with Jumper is a case in point of how each of you is coming from two different regulatory environments, you, David, NEC + Electric Utility, Jumper, NEC only.If there’s a water pipe and you need to add rods or such, what else would you call the rods?
This exchange with Jumper is a case in point of how each of you is coming from two different regulatory environments, you, David, NEC + Electric Utility, Jumper, NEC only.
The NEC does not require a ground rod as a grounding electrode. Period.
Correct it does not,
The NEC does not require metal reinforcing in footer neither,
The NEC does require it to be incorporated into the grounding electrode system if some other authority requires it to be there or if a builder places it there by choice
The NEC requires that if it is present it shall be bonded.
The NEC also requires a ground rod if it is present shall be bonded.
Almost 40 % of our single family dwellings do not have a metal water grounding electrode systems.
All of our buildings supplied by the utility have ground rods that are present.
I never said the NEC requires a ground rod I am saying a ground rod that is required to be present is required to become part of the grounding electrode system. It does not mater by what authority it becomes present only that it is present
It cannot be a rod to supplement a water line that is not there. So a ground rod that is required to be present by a utility Authority is a required grounding electrode by the NEC is it not?
A Supplemental electrode for a water pipe can connect to just about to anything the service neutral is connected too
A ground rod that is deemed to be present becomes part of the mandate to bond it to the grounding electrode system or connect it to the neutral with a grounding electrode conductor
David, no law is gonna say we have to do anything a POCO says. POCO can just not supply power to the place.
I live in an area that has a large Amish Community we have several homes without any Electric Service at all, not sure how that answer the question about a ground rod that is present
I do not understand. If a place has no electric, how is a ground rod involved?
I find it very hard to follow your train of thought. Are you suggesting that the above text says that a bonding jumper has to go from electrode to electrode? I don't see it, connecting the other electrodes via bonding jumpers to the grounding electrode conductor meets the above text. The use of the word "where" in the above text is not locational, it has the meaning "in the situation that".
Cheers, Wayne
You made the statement that no law could make you do what a Power Co regulates, I was one upping you and saying no law can make you install electric in your dwelling
the point i made in regards to the discussion how does what you said address a ground rod that is required to be present by an authority such as a utility
A utility is not an authority, it is just a business.
The only thing an a POCO can do is simply not supply power if the install does not meet their specs. An inspector has nothing to do with this.
Now if a POCO specs were included on EEs stamped drawings that were approved for the permit, then POCO specs would have to be met and inspection would include them.
The utility is given regulatory authority here by the state
Any utility given authority by the state is more than a business
but that doesn't mater when the ground rods are present,, the same as building steel being present, the same as steel in a footer being present, they are at every building because the utility reg, state they must be there
Is there anything in part 5 of this section that states a ground rod is to supplement a metal water pipe or the ground rod is being driven to supplement a metal water system electrode?But how does what happens in one state apply to the other forty nine?
You are confusing the crap out of me.
Is there anything in part 5 of this section that states a ground rod is to supplement a metal water pipe or the ground rod is being driven to supplement a metal water system electrode
Is there any thing other than it being present stated
III. Grounding Electrode System and Grounding Electrode Conductor
250.50 Grounding Electrode System.
All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shall be bonded together to form the grounding electrode system.
(5) Rod and Pipe Electrodes. Rod and pipe electrodes shall not be less than 2.44 m (8 ft) in length and shall consist of the following materials.
(a) Grounding electrodes of pipe or conduit shall not be smaller than metric designator 21 (trade size 3/4) and, where of steel, shall have the outer surface galvanized or otherwise metal-coated for corrosion protection.
(b) Grounding electrodes of stainless steel and copper or zinc coated steel shall be at least 15.87 mm (5/8 in.) in diameter, unless listed and not less than 12.70 mm (1/2 in.) in diameter.
Other than using rods as the sole electrodes for a GES, common in resi and small commercial, why would anyone drive rods other than to supplement a water pipe electrode?
Steel, CEE, and rings do not require additional electrodes.