radiopet said:.....I never hide anything as it is clearly on my site and in open public...![]()
You've been pretty good at hiding your site from me
radiopet said:.....I never hide anything as it is clearly on my site and in open public...![]()
Ok, ok, ok ...but how about for some of the other folks that don't have my mad skills?radiopet said:WHAT.....lol......now celtic you know it is in my profile....
Now we would do that?radiopet said:OH lord....do I dare post it for fear of Playful Razzing......ok..ok....www.theelectricalguru.com
Its too late...I switched to all fuses in place of breakers:grin:I just want Don to know....they are looking out for him and hope to make it all good very soon on the shallow promises of the old days....in fact I am hoping to load my entire panel up with AFCI's and do some testing if all goes right...
Even some details in that article are very misleading when you dig deep. They completely gloss over the fact that a very small percentage of the fires of electrical origin occur in dwelling units under 20 years old. The do not tell you that there is no reliable fire cause and origin data for most dwelling unit fires in the US. The cause for a very large number of these fires is listed on the fire report by the first due in company officer, a person with mimimal training in fire cause and origin. There is no way to know what type of electrical fault caused the fire and in many cases, because of errors in the fire investigation textbooks, non electrical fires are classified as electrical fires. One example is a text that said "if you see small rounded balls of copper on the wire the fire was caused by an electrical fault". Well these same small round balls of copper are formed when the fire from some other cause melts the insulation and permits a short to occur. Yes you can tell the difference in a lab, but it would be a very rare home fire where a sample is sent to a lab.Actually here is a GREAT article on the AFCI .....ENJOY - http://www.iaei.org/subscriber/magaz..._d/smittle.htm
don_resqcapt19 said:Its too late...I switched to all fuses in place of breakers:grin:
don_resqcapt19 said:Paul,
Even some details in that article are very misleading when you dig deep. They completely gloss over the fact that a very small percentage of the fires of electrical origin occur in dwelling units under 20 years old. The do not tell you that there is no reliable fire cause and origin data for most dwelling unit fires in the US. The cause for a very large number of these fires is listed on the fire report by the first due in company officer, a person with mimimal training in fire cause and origin. There is no way to know what type of electrical fault caused the fire and in many cases, because of errors in the fire investigation textbooks, non electrical fires are classified as electrical fires. One example is a text that said "if you see small rounded balls of copper on the wire the fire was caused by an electrical fault". Well these same small round balls of copper are formed when the fire from some other cause melts the insulation and permits a short to occur. Yes you can tell the difference in a lab, but it would be a very rare home fire where a sample is sent to a lab.
They strongly imply that most fires of electrical origin are caused by a parallel arcing fault. I don't believe that is the case. Most electrical fires occur at a point of connection. This type of fault produces heat with low current and no arcing and is not directly detected by an AFCI.
They cite a cost benefit by the CPSC but the homebuilders association cites a total different cost benefit.
They tell you that the branch circuit/feeder AFCI provides protection beyond the outlet, but fail to tell you that you must have at least 75 amps of fault current before the AFCI even looks at the arc. The end of many branch circuits, let alone the end of a 18-2 zip cord cannot supply 75 amps.
This whole thing is nothing more than a big snow job to pad the bottom line. If they don't make these things work as promised it may very well do the opposite. Once we have AFCI on all of the circuits and there are still fires of electrical origin, there should be a very large class action product liability suit that will remove the product from the market and punish the shareholders.
Don
Yes, I just don't like being lied to. They know exactly what they are doing. The details are all there when you dig deep enough, they just try to bury them deep enough so that you won't dig. Where ever I can, I will be advocating that the AHJs skip the 2008 NEC.lol....man you are bitter at em...thehehhee.....it's all good fella.
celtic said:I know you were making a joke....but is there any article in the NEC that would prohibut that on new construction?
Mike03a3 said:Umm - does Buss make AFCI fuses for the bedroom branch circuits?
celtic said:But say in the case of a small addition where the present service has glass fuses.....would you then be required to install a new panel that can accept AFCI OCPDs?
sparky_magoo said:I have never seen an AFCI receptacle. I have only been in this rural area for about three years. I still can't get used to the lax inspections around here. When we moved here, construction was booming. Now, it is really slow. Inspectors don't catch "squat" around here.
If any of you are interested, I will start a thread on some of the unbelievably stupid things I have been called on. Most of you probably wouldn't buy it!