Back in the day, the MWBC circuits did not need to be on the same breaker so they were technically two different circuits. You can still do this but a handle tie is required. Usually everyone just installs a 2-pole breaker.
Back in the day, there was not a rule that stated every circuit that shared a common neutral had to be "simultaneously disconnected" that is.
Without 2 or more "Ungrounded Conductors that have voltage between them" or "Ungrounded Conductors from 2 different phases" you have no MWBC.
JAP>