I guess 12-2-2 is the fix now....~RJ~
New loophole to get out of using AFCI's - only run MWBC's, and claim they are not "120 volt circuits"![]()
The beauty of 210.4(A) is that it gives us a choice. If we run a single MWBC for the small appliance branch circuits, and we want to consider it as two 120V circuits for compliance with 210.11(C)(1), great. Then the two circuits will need to comply with 210.12.If a 20 amp small appliance multi wire branch circuit is not two branch circuits than thousands of kitchens have been wired in violation and passed inspection by thousands of inspectors for 50 plus years
Sorry, where is the prohibition on installing a 125V receptacle on a 120/240V branch circuit? If there is one, I agree it would sink this line of thought.That would be a great loophole, except you wouldn't be able to install any 15A or 20A, 125V receptacles on the circuit, so the loophole is self defeating.
Sorry, where is the prohibition on installing a 125V receptacle on a 120/240V branch circuit? If there is one, I agree it would sink this line of thought.
Cheers, Wayne
I've got jap saying all the AHJs agree with him. Others saying AFCIs required.
406.4(A)
Jap never said anything about AFCI's not being required on a MWBC.
Only that a branch circuit is not a MWBC if it's strictly 120 volts.
JAP>
Are handle ties mandatory for multiple 1p breakers feeding a MWBC , or, just a requirement for all to have a means to be simultaneously disconnected ?
UL RTRT guideinfo says in part "Duplex receptacles rated 15 and 20 A that are provided with break-off tabs may have those tabs removed so that the two receptacles may be wired in a multi-wire branch circuit or multiple branch circuits."
So a duplex receptacle seems to be rated for the "voltage class" 120/240.
Cheers, Wayne
Actually, you quite clear said the converse: an MWBC is not a 120-volt circuit. Which in the context of my question would definitely mean that the arc fault requirement doesn't apply. But it seems you have never convinced an AHJ of that? Please clarify the record on that point, your responses now seem contradictory. :blink:
Not a means 'to be simultaneously disconnected'. A means 'that will simultaneously disconnect.' May seem subtle, but it means that simultaneity cannot be dependent on the user. Practically speaking, it means handle ties are required.
IMO, you are wrong.Only that a MWBC is not a 120v circuit,
AFCI requirement was never part of my statement.
Only that a MWBC is not a 120v circuit,or that a 120v circuit is not a MWBC. The circuit would have to have more than only 1 120v circuit to be a MWBC, otherwise there would not be one. K-wire Picked up on it when he stated 120/240v 120/208v or 277/480v. We do a lot of reading between the line where we're from.
And here I initially thought you were trying to give me a useful answer to my question. :roll::slaphead:
as far as the "To be simultaneously" or "That will simultaneously" disconnected, is going to require some type of "User" somewhere somehow to do either of them.
They aren't going to magically disconnect themselves now are they?
Jap>
I don't really want to go down this irrelevant tangent, but the point is that you cannot say that two separate breakers allow the user to simultaneously disconnect. The installation has to be such that they 'will' simultaneously disconnect when the user operates one or the other to do so.
IMO, you are wrong.
AFCI requirement was never part of my statement.
Only that a MWBC is not a 120v circuit,or that a 120v circuit is not a MWBC. The circuit would have to have more than only 1 120v circuit to be a MWBC, otherwise there would not be one. K-wire Picked up on it when he stated 120/240v 120/208v or 277/480v. We do a lot of reading between the line where we're from.
And here I initially thought you were trying to give me a useful answer to my question. :roll::slaphead:
I don't really want to go down this irrelevant tangent, but the point is that you cannot say that two separate breakers allow the user to simultaneously disconnect. The installation has to be such that they 'will' simultaneously disconnect when the user operates one or the other to do so.
And I dont really want to break the bad news to you that if the handle tie is actually not a requirement, then I could use 2 1p shunt trip breakers on whatever 2 opposing phases I want with a remote pushbutton and be good to go.
JAP>
IMO, you are wrong.
This thread is asking if AFCI protection is required for MWBC's. Your argument about someone wiring a three wire cable incorrectly is like a dog chasing it's tail.